For-Simplicity: ( L/N together ) as One , linked-together as the Regulations tells us L/N . & E

Between Live-conductors and Earth .

Minimum-insulation-résistance between Live-conductors , tested at 500V d.c. should not be less than 1MΩ .

Thismethod can be employed on a , periodic-test where installed-equipment is vulnerable to damage by thetest-voltage .

Main-switch in the On - position and all circuit-breakers closed .

• Between Live-conductor(s) separate - L . N . on there own .
Toensure that the readings obtained are , Accurate and therefore a true-reflection , of the condition of the conductors under-test .



 
From Old-Notes , not for exam purposes . Useful-Junk

Verification of Test-Results :

Itis a common-mistake for electricians to compare-test-results directly against those in BS-7671:2008

Themeasured-values of ( Zs ) of each final or distribution-circuit has to be in compliance , the obtained-values have to be compared against :

- Rule of thumb figures .
- Tabulated-values in Table . 41.2 . 41.3 . 41.4 . in BS-7671:2008 , these-values will have to be corrected for temperature . Or
- Table provided in Guidance-Note 3 .
- The Earth-fault-loop-impedance-values , provided by the designer .

Rule of Thumb-Figures : ( 0.8- 80%)

(Zs ) value at the remote-end of a circuit should not exceed ( 0.8 ) of the a appropriate-value inBS-7671

A Note-under Tables 41.2 . 41.3 . 41.4 . 41.6. States that
“ the circuit-loop-impedance ( Zs ) given in the tables should not be exceeded when theconductors are at their normal-operating-temperature , if the cables are at a different-temperature when tested “ the reading should be adjusted accordingly, see - Appendix14 .

Therequirements are satisfied if the , Measured ( Zs ≤ 0.8 x Uo / Ia ) i.e. 80% ofthe tabulated-values in BS-7671:2008

Determine whether the measured-values of earth-loop-impedance foreach-circuit satisfy the requirements of BS-7671:2008

Shower-circuit: BS-7671:2008 earth-loop-impedance Ω - 0.62 x 0.8 = 0.49 : Measured-value Ω - 0.50 : Pass or Fail .
Ring-final-circuit: BS-7671:2008 earth-loop-impedance Ω - 1.14 x 0.8 = 0.91 : Measured-value Ω - 0.84 : Pass or Fail .
Radial-sockets: BS-7671:2008 earth-loop-impedance Ω - 1.85 x 0.8 = 1.48 : Measured-value Ω - 1.36 : Pass or Fail .
Immersion-heater: BS-7671:2008 earth-loop-impedance Ω - 2.67 x 0.8 = 2.13: Measured-value Ω - 1.36 : Pass or Fail .
Lights- ( 1[SUP]st[/SUP] floor ) : BS-7671:2008 earth-loop-impedance Ω - 18.5 x 0.8 = 14.8: Measured-value Ω - 13.9 : Pass or Fail .
Lights- ( Gnd floor ) : BS-7671:2008 earth-loop-impedance Ω - 10.0 x 0.8 = 8.0: Measured-value Ω - 0.74 : Pass or Fail .

 
From Old-Notes , not for exam purposes. Useful-Junk

Verification of Test-Results :

It is a common-mistake for electricians tocompare-test-results directly against those in BS-7671:2008

The measured-values of ( Zs ) of each final ordistribution-circuit has to be in compliance , the obtained-values have to becompared against :

Tabulated-values in Tables - 41.2 . 41.4 . in BS-7671-2008 .


Two-factors , bothinvolving-temperature , must be taken into account when comparing any measured-value of ( Zs ) with the values obtained form BS-7671 :


i) Cable-operating-temperature-factor ( Assumed to be 70°C ) &
ii) The actual-temperature of theconductors when the measurement was taken , ( Usually-deemed to be the Ambient-temperature )

Conductor-operating-temperature-factor
The tabulated-value in BS-7671: are used for design-purposes and assume that the cables are attheir maximum-operating-temperature .

i.e. 70°C for thermoplastic - PVC/PVC . cables .

for comparison-purposes with BS-7671: the ambient-temperature at the time of the test is assumed to be 20°C .

i.e. using the temperature-coefficient of résistance for copper of , 0.004/°C , then the factor to adjust the measured-loop-résistance-value to what it would be at 70°C .

= 1 + [ 50 x 0.004/°C ] = 1.2 . for PVC - insulated-cables .

This factor is applied as a , multiplying-factor to be measured ( Zs - value ) then compared against the tabulated-value in BS-7671:2008:
Alternatively - the 1.2 can be used a divisor and applied directly to the tabulated-value in , BS-7671:2008: The measured-value can then be compared directly against this reduced-value .

Example : Determine whether the measurement taken at the socket-out for thecircuit shown complies with BS-7671:2008:

[ Table 41.3. type-B . BS-EN-60898 - 32A = 1.44 ] three-sockets , reading furthest-socket - ( 1.1 )

Using the method stated : Measured-value , x 1.2 = 1.1 x 1.2 = ( 1.32 )

Note : therefore , as the adjusted-measurement is less than , 1.44 it complies .

 
From-old-notes . 2008 .

Actual-conductor-temperature-factor

If themeasured-earth-fault-loop-Impedance-value , is taken at ambient-temperature Other than 20°C then it must be adjusted for the temperature-difference .

Example : Determine whether the measurement taken at the socket-outlet for thecircuit show-complies with BS-7671:2008:

32A -BS-EN-60898 Maximum- Zs 1.44Ω -

The ( 1.3Ω ) reading on the instrument has been Obtained at an , Ambient-temperature = 25°C .

Using the temperature-coefficient of résistance for copper of , 0.004Ω/°C , thenthe factor to adjust the measured-loop-résistance-value to what it would be at , 70°C

= 1 + [ ( 70 - 25) x 0.004Ω/°C ]
= 1 + [ 45 x 0.004Ω/°C ] = 1.18

From the table-provided :

Therefore , Reading at 70°C = 1.30 x 1.18 = 1.53Ω

As the measurement taken is greater than 1.44Ω then the circuit Does-Not-Comply .

Where the designer has provided test-values , they should have been compensated for the temperature-differences, thus enabling the Inspector to make a direct-comparison .







 
Earth-fault-loop-impedance:

State : four-points as described in Guidance-Note - 3 , where the measurement of earth-fault-loop-impedance is required to be taken .

i) at the supply-intake - ( Ze )
ii) at each distribution-board - ( Zdb ) GN-3
iii) at theremote-end of all finial-circuits - ( Zs)
iv) at each-socket-outlet - ( Zs )

indentify from the Four-points indentified above , reasons why these measurements are necessary .

i) at the supply-intake .

- to ensure the installation is effectively connected to Earth . -&-s big-time . 2394.
- to confirm that the actual ( Ze ) is equal to or less than what the designer has used in his design-calculations .

ii) at each-distribution-board ( Zdb )
- to enable the , prospective-earth-fault-current to be calculated .
- to confirm that the , protective-device supplying the distribution-board under earth-fault-conditions in thetime required by BS-7671:2011:
- in conjunction with either a visual-inspection , an ( Ra ) or a ( R[SUP]1[/SUP] + R[SUP]2[/SUP] )test , an earth--loop-impedance-test will confirm-polarity .

iii) at the remote-end of all-final-circuits ( Zs )
- to confirm that the protective-device supplying the final-circuit-disconnects under-earth-fault-conditions inthe time required by BS-7671:2011:

iv) at each-socket-outlet .
- to confirm that the protective-device supplying the socket-outlets disconnects under-earth-fault-conditions inthe time required by BS-7671:2011:

Identify ,Two-factors that the Inspector will have to consider when confirming his ,earth-fault-loop-impedance-measurements , are in compliance with the requirements of BS-7671:2011:

i) the normal-operating-temperature of the cables .
ii) the temperature of the cables at the time of test .

typical :electrical-installation(s) require an effective-connection to earth as part of the protective-system .

identify the Three most common , earthing-systems available to the District-Network-Organiser - ( DNO ) and state the , maximum-earthing-fault-loop-impedance at the supply-terminals for each-system .

i) TN-S . 0.80
ii) TN-C-S . 0.35
iii) TT - . 21 , from the DNO suppliers earth-electrode - Only . 21 + the consumers electrode-résistance .

you have an independent - earth-electrode - , from the-supplier

iii) TT - . 21 , O.S.G. p.11
TT - arrangement ,21 is the usual-stated-maximum-résistance of the distributions , earth-electrode at the supply-transformer . Etc .

Note: the résistance of the ( Consumers-installation-earth-electrode ) should be as low as practicable and a value exceeding 200 may not be stable .

Type of Protective-device : p.23 -O.S.G. RCBO - it can serve , under-fault-conditions . Overload : Short-circuit : Earth-fault. written-exams.

30mA RCD - is for Additional-protection only , theprotect the User . so its Additional . :gettree:





 
Values of (R1+R2) are measured :gettree:
Using an ohmmeter with a low range, such as 0to 20Ω, having a no-load voltage of between 4 V and 24 V, d.c. or a.c., and a short-circuit current ofnot less than 200mA (Regulation612.2.1 refers). The Q/A came up on the 2391 .
 
2394 : Written-exams .

Additional-protection:

Additional-protection by Residual-current-devices.

Theuse of an RCD whose rating ( IΔn ) does not exceed 30mA and disconnects within 40mS when tested at 5 x ( IΔn )

Is recognised as providing :

• Additional-protection against the failure of Basic-protection .
• Additional-protection against the failure of Fault-protection .
• Additional-protection against Carelessness by the User .

RCD-tester, must comply with BS-EN-61557-6
Leads to be in compliance with - GS-38

 
( G) non-delay RCD :

Q) for a 100mA non-delay RCD toBS-EN-61009-1 the residual-currents and maximum-permitted-disconnection-times , are .

a) 100mA - 300mS : 500mA - 40mS
b) 100mA - 130mS : 1500mA - 150mS
c) 100mA - 0mS : 100mA - 40mS
d) 100mA - 400mS : 500mA - 50mS

Q) The protective-measure , automatic-disconnection of supply . ( G) non-delay RCD :
a) is only permitted if the installation is under effective-supervision .
b) is a method of reducing thermal-effects .
c) is acombination of basic and fault-protection .
d) is a combinationof under and over-voltage-protection .

Q) An earth-fault-loop-impedance-test determines the actual-value of : a) Zs , b) Ze , c) R[SUP]1 [/SUP], d) R[SUP]2 [/SUP], The word - external was not Used . :gettree:

Earth fault loop impedance (Zs) is a characteristic vitalto the protective measure Automatic Disconnection of Supply (ADS),

The meaning of earth fault loop impedance
Earth-fault-loop-impedance (Zs) is theimpedance of the intended path of an earth fault current ( known as the earthfault loop )


 
GN-3p.66 . Requirements for Inspection & Testing .

Written-exams .
Q) What is the reason for a periodic-inspection. ? :christmaswreath:

3.8.1. Scope :
Thepurpose of periodic-inspection and testing is to provide an engineering-view on whether or not the installation is in asatisfactory-condition where it can continue to be used in a safe-way .

The periodic-inspectionand test-comprises a detailed-examination of the installation together with appropriate-tests .
The inspection is carried out without taking-apart or dismantling-equipment as far as is possible .

GN-3 are reminding us .
The tests made are mainly to confirm that thedisconnection-times-stated in Chapter -41 . are met , as well as highlighting-other-defects. Etc .

Q) On completionof periodic-testing an old-domestic-installation , theinsulation-résistance is found to belowthe requirements of BS-7671:2011: The immediate-action to be taken is to . ?

Notify thelocal-supply-authority
Notify the person-ordering the work
Put awarning-notice on the supply-intake-position
Protect thecircuits with smaller-sizes of fuses

Q) The Electricity at Work-Regulations 1989 concern’s its self with . ?
All aspects of electrical-systems
System up to 1000 volts
Special-locations only
High-voltage-systems only

2392-10 - 2394 :
Q) it is important to test a new-installation in the correct-sequence because . ?
The sequence is stated in GN-3
Each test relies on the previous to be correct
It is more-convenient
It is easy to remember

 
Old-notes 2002

Insulation-résistance, By calculations .

An installation comprising six-circuits have individual-insulation-résistance of : 2.5MΩ . 8MΩ . 200MΩ . 200MΩ . 200MΩ . 200MΩ.

Q ) So thetotal insulation-résistance will be .

1/Rt = 1/2.5 + 1/8 + 1/200 + 1/200 + 1/200 + 1/200 .

= 0.4 + 0.125 + 0.005 + 0.005 + 0.005 + 0.005 .

= 0.545

Rt = 1/0.545

= 1.83MΩ …… 1.0MΩ minimum but less than 2MΩ . ◄◄

This is clearly greater than the 1.0MΩ minimum butless than 2MΩ .

lessthan 2MΩ . ) are recorded then this might indicate a latent but not yet visible-fault in the installation. which would require further-investigation .

• If a value of less than 2MΩ is recorded it may indicate a situation where a fault isdeveloping .

Themore-resistances , there are in parallel, the lower the overall-résistance ,and in consequence , the longer a cable the lower the Insulation-résistance
Addto this the fact that almost all installation-circuits are also wired in parallel
 
this is the Question your likelyto get . 2392-10 / 2394.

Q) if each of the three-circuits had been tested individually and gave readings of - 80MΩ , 60MΩ , & 30MΩ respectively , what would be the expected overall insulation-résistance .

80MΩ , 60MΩ , 30MΩ ,

Q ) So thetotal insulation-résistance will be .
1/Rt = 1/80 + 1/60 + 1/30 .

= 0.0125 + 0.0166 + 0.033

= 0.0621 .

Rt = 1/ 0.621 = 16. , doingyour Calculation . where your decimal-point here . Yeah


a) 0.0625MΩ
b) 15MΩ
c) 16MΩ
d) 160MΩ
 
Q) the metal-partsof an building-structure are called : ? conductive-part liableto introduce a potential
earthing.
equipotential-bonding
exposed-conductive-parts
extraneous-conductive-parts

Regulations- p.28 .
Extraneous-conductive-parts A conductive-part liable tointroduce a potential , generally Earth-potential , and notforming part of the electrical-installation.

Q) the metal-parts of an electrical-installation notnormally-live are called : ?
earthing.
equipotential-bonding
exposed-conductive-parts
extraneous-conductive-parts

Regulations- p.27 .
Exposed-conductive-part Conductive-part of equipment which can be touched & which is notnormally-live , but which canbecome-live-under-fault-conditions .

Q) the process which maintains a potentialof zero-volts between all extraneous-exposed-conductive-parts is called : ?
earthing.
equipotential-bonding
exposed-conductive-parts
extraneous-conductive-parts

Q) the act of connecting exposed-conductive-parts to the earthing-terminal ofan installation is called : ?
earthing .
equipotential-bonding
exposed-conductive-parts
extraneous-conductive-parts

Q) the trunking & conduit of an electrical-installation are called : ?
thegeneral-mass of earth
thecircuit-protective-conductor - ( CPC)
exposed-conductive-parts
extraneous-conductive-parts

Exposed-conductive-part Conductive-part of equipment which can be touched & which is notnormally-live , but which canbecome-live-under-fault-conditions .

Q) an electrical-connectionwhich maintains exposed-conductive-parts & extraneous-conductive-parts atthe same-potential is called : ?
(CPC ) - circuit-protective-conductor
earth-conductors
protective-equipotential-bonding : equipotential-bonding for thepurposes of safety .
supplementary-bonding

 
Re-cap. 2392-10 , 2394.

Résistance in Series :

These are resistance joined , end to end in the form of a chain .

The total-resistance-increases as more-resistances are added .

Hence: if a cable-length is increased , its résistance will increase in proportion .

Example: 100m length of conductor has twice the résistance of a 50m length of the same-diameter .

1/R[SUP] total [/SUP] = 1/R[SUP]1[/SUP] + 1/R [SUP]2[/SUP]+ 1/R[SUP]3[/SUP] + 1/R[SUP]4 [/SUP]

1Ω - ( R[SUP]1[/SUP]) 2Ω - ( R[SUP]2[/SUP]) 10Ω - ( R[SUP]3[/SUP]) 4Ω - ( R[SUP]4[/SUP] ) Ω .

R[SUP] total [/SUP] = 1 + 2 + 10 + 4 = 17Ω

Résistance in parallel .

These are résistance joined like therungs of a ladder . here the total-résistance-decreases .

1/R[SUP] total [/SUP] = 1/R[SUP]1[/SUP] + 1/R [SUP]2[/SUP] + 1/R[SUP]3[/SUP] + 1/R[SUP]4 [/SUP]
[SUP] [/SUP]
3Ω - 6Ω - 8Ω - 2Ω

1/R[SUP] total [/SUP] = 1/R[SUP]1[/SUP] + 1/R [SUP]2[/SUP] + 1/R[SUP]3 [/SUP] + 1/R[SUP]4 [/SUP]

= 1/3 + 1/6 + 1/8 + 1/2

= 0.333 + 1.167 + 1.125 + 0.5

Therefore: = 1/1.125 .

High-value-resistances’ inparallel . hence : anincrease in cable-length-results in a decrease in insulation-résistance.

This value is measured in millions of ohms . - megohms ( MΩ )

Watch you Questions shown in words . :mad2:

• If youthen do the full-calculation using the ( Un-round up figures ) 1.125 .
• In exams , you will have to ( Roundit up ) exactly 16M . 100M .

 
BS-7671:2008/ 2011: Basic principles of : Protection against !!

Protection against Electric-Shock . Part-4 . ( So in theory , Principles of Electric-Shock protection )

Electric-Shock occurs when a person becomes a part of the electrical-circuit .

Methodsused , keep-people away from Live-electrical-equipment. it is called - Basic-Protection . 131.2.1.

► Consumer-Unit , ( 2392-10 . Why do we use Class - 11 enclosure on all Installations now . Protection for the User ) N/A, Touching exposed-conductive-parts .

Basic-Protection . Protection against Electric-Shock. under fault-free-conditions .

By- Definition : p.23. Basic-Protection.
Note : for low-voltage-installations , systemand equipment , basic-protection generally-corresponds to ( Protection against ) direct-contact, that is

contact of persons or livestock with live-parts

Re-cap: Indirect-contact:
Touching exposed-conductive-parts , such as themetal-work of an appliance . whichhas become live as a result of a fault . The potential-voltage on this metalwork rises above earth-potential , electric-shock may occur when someone-touches the metalwork .

By- Definition : p.28. Fault-Protection.
Note : for low-voltage-installations , systems and equipment , fault-protection generally corresponds to ( Protection against ) indirect-contact. mainly with regards to failure of ,basic-insulation ,

Indirect-contactis , contact of persons or livestock with exposed-conductive-parts which have become-live under fault-conditions

Protection against touching something made live as a result of a fault , is called fault-protection , and is achieved by protective-equipotential-bonding & automatic-disconnection of the supply - ( ADS ) in the event of a fault-occurring , 131.2.2.

O.S.G. p23 . Types of protective-device .

RCBOs- will minimize-inconvenience in theevent of a fault and is applicable toall systems , TN-S , TT -
Theconsumer-unit contains devices for the protection of final-circuit(s) against : Overload , Short-circuit , Earth-fault . ( Electronic to trip the contacts )

RCBO- Small-white-flylead which connect to Earth , either D.C.. sensing or A.C. sensing .
Modern - RCBOs have a cream-wire which connects to earth known as a functional-earth .
Modern - RCBOs some - facts , generally the ones with a functional-earth use ( Electronic to trip the contacts ) as Opposed to just using ( Coils )

RCD- is used to provide Additional-protection, against electric-shock and the earthing-system is there to keep all ( Exposed / Extraneous-conductive-parts - ( Surfaces ) at or about the same-potential in the event of a fault , & to clear the fault-quickly byoperating the Protective-device .

Protective-device(s) Genetic-name for : :gettree: :17:
Fuse .
Circuit-breaker .
RCD . to improve-safety .
RCBO - MCB /RCD .






 
Protective-equipotential-bonding

Is equipotential-bonding for the purpose of safety , theapplication of protective-equipotential-bonding to earth is one of theimportant-principles for safety .
Regulation- 131.2.2.

p.17. inconnection with fault-protection , theapplication of the method of protective-equipotential-bonding isone of the important-principles for safety . :santa5:


 

Reply to Re-take - Useful Information for 2394 : in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

thanks for the confirmation this is what i thought. i cant think of what use this device is . i have seen David Saverys Arc Fault Detection Device...
Replies
4
Views
376
  • Question
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top