Useful-Junk:
Earth-fault-loop-impedance: 612.9. ( Circuit-loop-impedance )
The method of testing involves connecting the tester between Line & Earth .
When the test is started , a current is passed around the circuit and supply and the loop-impedance ismeasured .
Some-tester(s) use a , 2 - lead-connection
While some use 3 - leads
The only-difference is that the , 2 - lead-tester , powers the instrumentfrom Line and Earth , whilst the 3 - lead-tester uses the Neutral , the Neutral-connection can simply be connected to Earth and it will then behave as a 2 - lead-tester .
Table- 41.5.
The Regulations require only that ( Zs) does not exceed 50V ÷ by thenominal-rating of the RCD .
100mA device this would be 500Ω ,
30mA device would be 1667Ω , 50V ÷ 30mA = 1667Ω
30mA ÷ 1000 = 0.03A .
50V ÷ 0.03A = 1667Ω .
( Circuit-loop-impedance ) 612.9. Earth-fault-loop-impedance :
Where protective-measures are used whichrequire a knowledge of earth-fault-loop-impedance . the relevant-impedance(s) shallbe measured . :icon_bs:
[h=1]Blast from the past : ◄ [/h][h=1]Avoiding unwanted tripping of RCDs and circuit-breakers whenmeasuring Zs [/h]Earth fault loop impedance testinstruments using techniques other than conventional high-current testing arerequired to prevent tripping of RCDs and certain types of circuit-breaker
Many earth fault loopimpedance test instruments use a test measuring current of between 20 A and 25 A. This test current can flow inthe earth fault loop for, typically, 40 ms. This relatively high current willusually trip any RCD protecting thecircuit and may also trip some circuit-breakers, suchas Type B overcurrent circuit-breaker to BS EN 60898 having a rated current less than 10 A.
This unwanted operation of a protective device will prevent themeasurement of earth fault loop impedance from being taken and, perhaps moreimportantly, result in an unwanted disconnection of the supply to the circuitunder test.
Solution
The value of earth fault loop impedance (Zs) is required to bedetermined for every distribution circuit and final circuit having AutomaticDisconnection of Supply (ADS) as its protective measure against electric shock.The value of Zs is also one of the values required to be recorded on theSchedule of Test Results in the Electrical Installation Certificate andPeriodic Inspection Report.
Regulation 612.9 indicates that the value of Zs may bedetermined by direct measurement or by an alternative method.
Instrument manufacturers can supply earth fault loop impedancetest instruments that are less liable to trip RCDs and circuit-breakers than isthe case with a conventional high current earth fault loop impedance testinstrument. There are two common techniques that manufacturers employ:
• d.c. biasingthe RCD: this techniqueusers a d.c. bias current to saturate the core of the RCD prior to the testsuch that the actual Zs measuring test current is undetected by the RCD. (It isimportant to remember that this technique is not effective for all types of RCD)
• Testing a reduced current : this technique uses a test current at or below 15mA, suchthat RCDs having a rated residual current of 30mA and greater will not trip. This techniquewill also mean that overcurrent circuit-breakers of Type B with a rated currentless than 10 A should not trip when measuring Zs.
612.9. Earth-fault-loop-impedance :
Where protective-measures are used whichrequire a knowledge of earth-fault-loop-impedance . the relevant-impedance(s) shallbe measured . or determined by an alternative-method .
Earth-fault-loop-impedance: 612.9. ( Circuit-loop-impedance )
The method of testing involves connecting the tester between Line & Earth .
When the test is started , a current is passed around the circuit and supply and the loop-impedance ismeasured .
Some-tester(s) use a , 2 - lead-connection
While some use 3 - leads
The only-difference is that the , 2 - lead-tester , powers the instrumentfrom Line and Earth , whilst the 3 - lead-tester uses the Neutral , the Neutral-connection can simply be connected to Earth and it will then behave as a 2 - lead-tester .
Table- 41.5.
The Regulations require only that ( Zs) does not exceed 50V ÷ by thenominal-rating of the RCD .
100mA device this would be 500Ω ,
30mA device would be 1667Ω , 50V ÷ 30mA = 1667Ω
30mA ÷ 1000 = 0.03A .
50V ÷ 0.03A = 1667Ω .
( Circuit-loop-impedance ) 612.9. Earth-fault-loop-impedance :
Where protective-measures are used whichrequire a knowledge of earth-fault-loop-impedance . the relevant-impedance(s) shallbe measured . :icon_bs:
[h=1]Blast from the past : ◄ [/h][h=1]Avoiding unwanted tripping of RCDs and circuit-breakers whenmeasuring Zs [/h]Earth fault loop impedance testinstruments using techniques other than conventional high-current testing arerequired to prevent tripping of RCDs and certain types of circuit-breaker
Many earth fault loopimpedance test instruments use a test measuring current of between 20 A and 25 A. This test current can flow inthe earth fault loop for, typically, 40 ms. This relatively high current willusually trip any RCD protecting thecircuit and may also trip some circuit-breakers, suchas Type B overcurrent circuit-breaker to BS EN 60898 having a rated current less than 10 A.
This unwanted operation of a protective device will prevent themeasurement of earth fault loop impedance from being taken and, perhaps moreimportantly, result in an unwanted disconnection of the supply to the circuitunder test.
Solution
The value of earth fault loop impedance (Zs) is required to bedetermined for every distribution circuit and final circuit having AutomaticDisconnection of Supply (ADS) as its protective measure against electric shock.The value of Zs is also one of the values required to be recorded on theSchedule of Test Results in the Electrical Installation Certificate andPeriodic Inspection Report.
Regulation 612.9 indicates that the value of Zs may bedetermined by direct measurement or by an alternative method.
Instrument manufacturers can supply earth fault loop impedancetest instruments that are less liable to trip RCDs and circuit-breakers than isthe case with a conventional high current earth fault loop impedance testinstrument. There are two common techniques that manufacturers employ:
• d.c. biasingthe RCD: this techniqueusers a d.c. bias current to saturate the core of the RCD prior to the testsuch that the actual Zs measuring test current is undetected by the RCD. (It isimportant to remember that this technique is not effective for all types of RCD)
• Testing a reduced current : this technique uses a test current at or below 15mA, suchthat RCDs having a rated residual current of 30mA and greater will not trip. This techniquewill also mean that overcurrent circuit-breakers of Type B with a rated currentless than 10 A should not trip when measuring Zs.
612.9. Earth-fault-loop-impedance :
Where protective-measures are used whichrequire a knowledge of earth-fault-loop-impedance . the relevant-impedance(s) shallbe measured . or determined by an alternative-method .