2392:10 . Designer(s) Installer(s) , first of all you have to decide what you are trying to Achieve & Why.
The O.S.G. section3 . P/25 Guidance :
The requireddisconnection times for TT – systems can ( except in most exceptional circumstances ) Only be achieved byprotecting every-circuit with an RCD .
Electrode-résistance inTT – system(s) 411.5.3. P/57
The Regulations requirethat the earth-résistance at the electrode ( Ra or Zs ) be as low as practicable . Table – 41.5.
States that: 41.5. specifies a maximum-résistance required for a ( 30mA RCD ) to comply is 1.667Ω *
Note 2 : * The résistanceof the installation earth-electrode should be as low as practicable .
Note 2 : A valueexceeding 200Ω may not be stable .
RCD / 30mA earth-current would trip the device within the required ( 0.2s ) conditions comply with 411.5.3.
Fault disconnectiontimes for, TN – TT – systems
BS-7671:2011: specify the requirements forAutomatic-Disconnection of Supply . byprotective-device(s) circuit-breaker(s)of a fault occurring .
BS-7671:2011: disconnection time ( fault’s Occurring )
BS-7671: have statedthe facts . Type of Earthing-systems ?? You , decidewhat you are trying to Achieve & Why.
P/53 , Regulation 41.1. “ Stipulates “ Maximum-disconnection-times
Typeof Earthing-systems
Circuits rated , 32A or less , TN – installation(s) must disconnect within ( 0.4s ) 400mS
Circuits rated , over 32A , TN – installation(s) must disconnect within ( 5s )
Circuits rated , 32A or less , TT – installation(s) must disconnect within ( 0.2s ) 200mS
Circuits rated , over 32A , TT – installation(s) must disconnect within ( 1.0s )
2392-10 : Where does BS-7671:2011: “ Start “
Metal-clad or Plastic all insulated consumer-unit ? What makes thedifference in the eyes of BS-7671:2011 & O.S.G.
Re-cap : 2392-10 : P/29 / O.S.G. The Enclosures of RCDs
Or consumer-units incorporating RCDs in TT – installation(s) should have an ( All-insulated or Class-11 construction oradditional-precautions )
Out of curiosity, Whydoes an RCD allow for a ( Zs of 1667Ω ) P/57 / Table 41.5.
[ I = V/R , R = V/R , 50V maximum-touch-voltage ] / 0.03 ( 30mA ) = 1667Ω :
50V ÷ 30mA = 1.666666667Ω [ round – up to 1667Ω ]
[ 30mA ÷ 1000 = 0.03A]
O.S.G. P/23, ( Protection)
Firstly : Type of protective-devices
The consumer-unit ( or distribution-board ) contains devices for the ( Protection) of distribution-circuits & final-circuits against .
• Overload .
• Short-circuit .
• Earth-fault .
2392-10 : Circuit-breaker & RCBOs don’t stop at , BS-EN.
Stillout there . ( Overload-protection ) BS-3871, O.S.G. P/23
Appx 3 , 533.1. Overload-protection will be provided by the ( Use) of any of the following devices .
Fuses to BS-88-2 , BS-88-3 , BS-88-6 , BS-1361 & BS-3036 .
Under the 16[SUP]th[/SUP] Edition they where called this , Miniature – circuit - breakers to BS-3871-1 types ( 1 , 2 , & 3 )
Circuit-breaker(s) to BS-EN-60898 types , B , C , & D .
Residual-current-circuit-breaker(s) ( With ) integral-overcurrent-protection ,RCBOs, to BS-EN-61009-1