BS-7671:2011; & GN-3 . wouldany of this come up on Exams . ( Everytest has it’s Merits ) :icon_bs:
C&Gs / GN-3,Stipulates that, The installation must remain isolatedfrom the ( Supply ) until alltesting has been completed & the earth-electrode connection-reinstated .
C&Gs / GN-3,Stipulates that, This disconnection will ensure that thetest-current Only passes through the, earth-electrode and not through any ( Parallel-paths )
( Where-required )
Re-cap : 612.7. Earth-electrode-résistance.
BS-7671: Stipulatesthat where, earth-electrodes are usedthey should be tested. BS-7671: Electrode-resistance to Earth shall be measured
If the electrode under test forms part of the earth-return for a TT – system in conjunction with an RCD, GN-3 describes the following method(s) .
• Disconnect theinstallation-protective-equipotential-bonding ( equipotential / equal bonding ) from the earth-electrode to ensurethat the test current passes only through the earth-electrode .
• Switch off the consumer’s unit to isolate theinstallation
• Using a Earth-loop-impedance-tester, testbetween the incoming line-conductor and the earth-electrode . BS-EN-61557-3 Instruments conforming .
• Reconnect : theprotective-bonding-conductor(s) when the test is completed .
Record the results on a, Schedule of test-results , accordingto Appendix - 6 , BS-7671:
GN-3 : stipulates that, that an acceptable value for the measurement of the earth-electrode-résistance, would be less that 200Ω .
BS-7671:2011: P/57 . Table 41.5 . Note – 2 *: The résistance of the installationearth-electrode should be as low as practicable. A value exceeding 200Ω may not be stable. Refer toregulation 542.2.4. The type & embedded depth of an earth-electrode . Etc
Supply Connected .
Testing earth-fault-loop-impedance :
Your object of this test is to ( Verify) that the impedance of the whole ( earth-fault-current-loop ) islow enough to allow the overcurrent-protective-device to operate within the disconnection timerequired Stated in BS-7671:2011: in our case here Table 41.3. RCBO / Circuit-breakers .
P/36 . Verification : All measures by means of which compliance of the electrical-installationwith the relevant requirements of BS-7671:are checked .
Comprising . Inspection , Testing & Certification .
“ Competent-person “
612.9. Earth-fault-loop-impedance . ( 2392-10 , Circuit-loop-impedance )
Where protective-measuresare used, which require knowledge of earth-fault-loop-impedance, the relevant-impedancesshall be measured .
GN-3 . Re-cap . Protection by automatic-disconnection of supply . P/51.
The effectiveness of measures for fault-protectionby ( ADS ) can be verified for installation(s) with a TN – system by :
• Measurement of earth-fault-loop-impedance .
2392-10 , Reason :- youhave confirmed that you have an Earth before testing your RCDs / RCBOs
• Confirmation by visual-inspection that , overcurrent-device have suitableshort-time or instantaneous tripping setting forcircuit-breakers,
• where RCDs are employed, testing to confirm that thedisconnection-times of Chapter 41 . of BS-7671:can be met .
RCDs :- Residual - dual / Line & Neutral-conductor(s) Two / dual in Balance :rant:
C&Gs / GN-3,Stipulates that, The installation must remain isolatedfrom the ( Supply ) until alltesting has been completed & the earth-electrode connection-reinstated .
C&Gs / GN-3,Stipulates that, This disconnection will ensure that thetest-current Only passes through the, earth-electrode and not through any ( Parallel-paths )
( Where-required )
Re-cap : 612.7. Earth-electrode-résistance.
BS-7671: Stipulatesthat where, earth-electrodes are usedthey should be tested. BS-7671: Electrode-resistance to Earth shall be measured
If the electrode under test forms part of the earth-return for a TT – system in conjunction with an RCD, GN-3 describes the following method(s) .
• Disconnect theinstallation-protective-equipotential-bonding ( equipotential / equal bonding ) from the earth-electrode to ensurethat the test current passes only through the earth-electrode .
• Switch off the consumer’s unit to isolate theinstallation
• Using a Earth-loop-impedance-tester, testbetween the incoming line-conductor and the earth-electrode . BS-EN-61557-3 Instruments conforming .
• Reconnect : theprotective-bonding-conductor(s) when the test is completed .
Record the results on a, Schedule of test-results , accordingto Appendix - 6 , BS-7671:
GN-3 : stipulates that, that an acceptable value for the measurement of the earth-electrode-résistance, would be less that 200Ω .
BS-7671:2011: P/57 . Table 41.5 . Note – 2 *: The résistance of the installationearth-electrode should be as low as practicable. A value exceeding 200Ω may not be stable. Refer toregulation 542.2.4. The type & embedded depth of an earth-electrode . Etc
Supply Connected .
Testing earth-fault-loop-impedance :
Your object of this test is to ( Verify) that the impedance of the whole ( earth-fault-current-loop ) islow enough to allow the overcurrent-protective-device to operate within the disconnection timerequired Stated in BS-7671:2011: in our case here Table 41.3. RCBO / Circuit-breakers .
P/36 . Verification : All measures by means of which compliance of the electrical-installationwith the relevant requirements of BS-7671:are checked .
Comprising . Inspection , Testing & Certification .
“ Competent-person “
612.9. Earth-fault-loop-impedance . ( 2392-10 , Circuit-loop-impedance )
Where protective-measuresare used, which require knowledge of earth-fault-loop-impedance, the relevant-impedancesshall be measured .
GN-3 . Re-cap . Protection by automatic-disconnection of supply . P/51.
The effectiveness of measures for fault-protectionby ( ADS ) can be verified for installation(s) with a TN – system by :
• Measurement of earth-fault-loop-impedance .
2392-10 , Reason :- youhave confirmed that you have an Earth before testing your RCDs / RCBOs
• Confirmation by visual-inspection that , overcurrent-device have suitableshort-time or instantaneous tripping setting forcircuit-breakers,
• where RCDs are employed, testing to confirm that thedisconnection-times of Chapter 41 . of BS-7671:can be met .
RCDs :- Residual - dual / Line & Neutral-conductor(s) Two / dual in Balance :rant: