OP
amberleaf
Extract's from 2009 / 2391 .
Working my way around the Guidance Note 3 . learning curve
Q) Three items to be checked , as identified on the Schedule of Inspections , where fault-protection is provided by automatic disconnection of supply ( ADS )
GN-3 P/20 . Method 1 : automatic disconnection of the supply ( ADS )
You're Q , Presence of appropriate protective-conductor(s)
542.3. Earthing conductor .
Sect 543. Circuit-protective-conductor(s)
Sect 544. Protective bonding conductors
- main bonding conductors
- supplementary bonding conductors .. ( where required )
312.2. The earthing system must be determined e.g.
► TN-C-S system ( protective multiple earthing ( PME))
► TN-S system
► TT system ( earth electrode(s)
411.4.5. The earth fault loop impedance must be appropriate for the protective device i.e. RCD or overcurrent device .
GN-3 P/97 . Schedule of Inspection ( for new installation work only )
Fault protection
i) Automatic disconnection of supply
You're Q . Check for Presence of :
(✓) Presence of earthing conductor
(✓) Presence of circuit-protective-conductors
(✓) Presence of protective-bonding-conductors
Choice of protective devices . ? Circuit-breaker , RCD / RCBO .
Additional protection:
(✓) Presence of resi/dual current devices(s)
O.S.G. P/85/86 Inspection :
9.2.2. Inspection checklist , viii ( d 415.1. additional protection by RCDs )
Working my way around the Guidance Note 3 . learning curve
Q) Three items to be checked , as identified on the Schedule of Inspections , where fault-protection is provided by automatic disconnection of supply ( ADS )
GN-3 P/20 . Method 1 : automatic disconnection of the supply ( ADS )
You're Q , Presence of appropriate protective-conductor(s)
542.3. Earthing conductor .
Sect 543. Circuit-protective-conductor(s)
Sect 544. Protective bonding conductors
- main bonding conductors
- supplementary bonding conductors .. ( where required )
312.2. The earthing system must be determined e.g.
► TN-C-S system ( protective multiple earthing ( PME))
► TN-S system
► TT system ( earth electrode(s)
411.4.5. The earth fault loop impedance must be appropriate for the protective device i.e. RCD or overcurrent device .
GN-3 P/97 . Schedule of Inspection ( for new installation work only )
Fault protection
i) Automatic disconnection of supply
You're Q . Check for Presence of :
(✓) Presence of earthing conductor
(✓) Presence of circuit-protective-conductors
(✓) Presence of protective-bonding-conductors
Choice of protective devices . ? Circuit-breaker , RCD / RCBO .
Additional protection:
(✓) Presence of resi/dual current devices(s)
O.S.G. P/85/86 Inspection :
9.2.2. Inspection checklist , viii ( d 415.1. additional protection by RCDs )