Ask the Question , What can Guidance Note 3 do for YOU. :svengo: It’s a must in any Exams’
a) List two methods utilised for Basic protection ... usually provided by insulation and / or enclosures
â–ş GN-3 - 2008: Basic protection 416
Insulation of live parts
Although protection by insulation is the usual method , there are other basic protection methods . 416.1.
Barriers or enclosures
Where live parts are protected by barriers or enclosures , these should be checked for adequacy and security . 416.2.
â–ş GN-3 - 2011: P/19 . Basic protection 416
Basic protection is most usually provided by insulation and / or enclosures . The inspection of this measure is to check that insulation has not been damaged during installation and that enclosures have been selected for at least IPXXB or IP2X and , for top surfaces , at least IPXXD or IP4X , and are not damaged . ( Insulation résistance is of course a fundamental test to be carried out )
b) List one method utilised for Fault protection
â–ş GN-3 - 2011: P/19 . Fault protection Sec 411 ( 1 )
Fault protection
The various methods of fault protection are classified in a number of subsections in BS-7671: and are :
( 1 ) Automatic disconnection of supply .
P/20 . Method 1 .
Automatic disconnection of supply ( ADS )
For each circuit , automatic disconnection is required and , although the main part of verification is measurement of earth fault loop impedance in order to confirm disconnection times , there are inspection aspects to consider for verifying ADS as follows :
Presence of appropriate protective conductor(s)
Earthing-conductor
Circuit-protective-conductors
Protective bonding conductors
- Main bonding conductors
- Supplementary bonding conductors ( where required )
312.2. The earthing system must be determined e.g.
TN-C-S ( Protective multiple earthing ( PME ))
TN-S system
TT system ( earth electrode(s))
411.4.5. The earth fault loop impedance must be appropriate for the protective device , i.e. RCD or Overcurrent device .
BS-7671:2011: P/23 :icon_bs:
Basic protection .
Protection against electric shock under fault-free conditions .
Note : For low voltage installations , systems and equipment, basic protection generally corresponds to protection against direct contact , that is “ contact of person or livestock with live parts “
BS-7671:2011: P/28 :icon_bs:
Fault protection .
Protection against electric shock under single fault conditions .
Note : For low voltage installations , systems and equipment , fault protection generally corresponds to protection against indirect contact , mainly with regards to failure of basic insulation .
Indirect contact is “ contact of persons or livestock with exposed-conductive-parts which have become live under fault conditions “
411 Protective Measure : Automatic Disconnection of Supply .
(ii) fault protection is provided by protective earthing , protective equipotential bonding and automatic disconnection in case of a fault . refer
410.3.3. The following protective measures generally are permitted :
(i) Automatic disconnection of supply - section 411.1.
P/51 Note : In electrical installations the most commonly used protective measure is automatic disconnection of supply .