My main point is to make you aware of the (( :skep: THREE-STEPS TEST )) -&-s .. to verify the continuity , (( Ring-final-circuits ))
Step 2 . ((Cross connect )) Line and Neutral
GN-3 reminds us : The open ends of the Line & Neutral conductor(s) are then connected together so that the outgoing Line-conductor is connected to the returning Neutral-conductor and vice versa (( refer to Figure 2.2b )) P/37 connecting for testing Step 2 .
• Measure between Line-conductor and Neutral-conductor at each socket-outlet .
Values should be the same at each socket-outlet .. should be ( r[SUP]1[/SUP] + r[SUP] N[/SUP] ) / 4
Step 3 . ((Cross connect )) Line and Circuit-protective-conductors
• Measure between Line-conductor and Circuit-protective-conductors at each socket-outlet .
Values should be the same at each socket-outlet .. should be ( r[SUP]1[/SUP] + r[SUP] 2[/SUP] ) / 4
(( refer to Figure 2.2c )) P/37 connecting for testing Step 3 .
Value is recorded as ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) on the . (( Am using the wording - Generic Schedule of Test Results ) -&-s GN-3 & BS-7671: States this
R/P402 . Continuity ( Ω ) ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) 13 .
You have proven continuity long before now . Step 1 : Little r[SUP]S[/SUP] ( r[SUP]1[/SUP] , r[SUP] N[/SUP] , r[SUP]2[/SUP] )
This is still a Dead test :- Why is it ( r[SUP]1[/SUP] + r[SUP] 2[/SUP] ) / 4
By Cross connecting the opposing Lines and circuit-protective-conductors creates a perfect resistive circle
( By Cross connecting the ) Lines and circuit-protective-conductors , resistances are in parallel
As GN-3 reminds us .
A higher résistance value will be recorded at any Socket-outlet wired as Spurs . (( watch this in Exams Q/As ))
Schedule of Test Results :leaving:
The value can be used to determine the earth-fault-loop-impedance ( Zs system ) of the circuit to verify compliance with the loop impedance requirements of the Regulations
Step 2 . ((Cross connect )) Line and Neutral
GN-3 reminds us : The open ends of the Line & Neutral conductor(s) are then connected together so that the outgoing Line-conductor is connected to the returning Neutral-conductor and vice versa (( refer to Figure 2.2b )) P/37 connecting for testing Step 2 .
• Measure between Line-conductor and Neutral-conductor at each socket-outlet .
Values should be the same at each socket-outlet .. should be ( r[SUP]1[/SUP] + r[SUP] N[/SUP] ) / 4
Step 3 . ((Cross connect )) Line and Circuit-protective-conductors
• Measure between Line-conductor and Circuit-protective-conductors at each socket-outlet .
Values should be the same at each socket-outlet .. should be ( r[SUP]1[/SUP] + r[SUP] 2[/SUP] ) / 4
(( refer to Figure 2.2c )) P/37 connecting for testing Step 3 .
Value is recorded as ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) on the . (( Am using the wording - Generic Schedule of Test Results ) -&-s GN-3 & BS-7671: States this
R/P402 . Continuity ( Ω ) ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) 13 .
You have proven continuity long before now . Step 1 : Little r[SUP]S[/SUP] ( r[SUP]1[/SUP] , r[SUP] N[/SUP] , r[SUP]2[/SUP] )
This is still a Dead test :- Why is it ( r[SUP]1[/SUP] + r[SUP] 2[/SUP] ) / 4
By Cross connecting the opposing Lines and circuit-protective-conductors creates a perfect resistive circle
( By Cross connecting the ) Lines and circuit-protective-conductors , resistances are in parallel
As GN-3 reminds us .
A higher résistance value will be recorded at any Socket-outlet wired as Spurs . (( watch this in Exams Q/As ))
Schedule of Test Results :leaving:
The value can be used to determine the earth-fault-loop-impedance ( Zs system ) of the circuit to verify compliance with the loop impedance requirements of the Regulations