2015 - O.S.G. 2.2.6. Consumer unit assemblies :book: :svengo:
421.1.201 Where a consumer unit is installed in domestic (household ) premises, domestic garages and outbuildings, one of the following applies:
► the enclosure manufactured from non-combustible material, or
► the consumer unit is enclosed in a cabinet constructed from non-combustible material
Note: This requirement will be effective from 1[SUP]st[/SUP] January 2016, although implementation before this date is not prohibited.
Ferrous metal, i.e. steel is deemed to be an example of a non-combustible material.
plastic enclosures manufactured from 960 degree glow-wire rated material would NOT be classified as “ non-combustible material ” in the context of this regulation .
Where a steel consumer unit is installed in an installation forming part of a TT system, the earth fault loop impedance Ze, is likely to be much higher than that permitted by the overcurrent protective device, i.e. cut-out. Should the tails become loose or damaged and make contact with the metal enclosure, it is likely that the overcurrent device will NOT operate within 5s . The IETs Wiring Regulations Policy Committee, therefore, advises the following:
(a) Consideration should be given to the selection and installation of a class 11 metal consumer unit when used on installation(s) forming part of a TT system. The consumer unit must have been validated as non-combustible using an appropriate test method such as an internal hot wire test and that the metal enclosure does not make contact with any line conductors in the event of an internal fire. Individual manufactures will be able to advice on products which meet these requirements, or
(b) A Class 1 metal consumer unit is installed and each outgoing circuit is protected by an RCBO.
(c) A split, Class1 metal consumer unit is installed, where the double-pole main switch of the consumer unit should incorporate an S type ( time delayed ) RCCB ,e.g. 100mA S - type RCCB.
Note: In cases where RCBOs protect each outgoing circuit. the risk of the solid busbar ( connecting the supply side of each RCBO ) making contact with the ferrous enclosure is minimal. In split consumer units, where two or three RCCBs protect multiple circuits through individual circuit-breakers, the risk of the single-insulated conductors ( connecting the load side of the double-pole main switch to the supply side of the RCCBs) making contact with the ferrous enclosure due to vibration and / or abrasion or being damaged is far higher. In essence, where the construction and layout of the consumer unit is such that the risk of live conductors making contact with the ferrous enclosure is minimal, then the double-pole main switch need not incorporate an S - type RCCB.
In all cases:
522.8.1.
(a) the tails need to be protected to avoid mechanical damage and disturbance at the incoming terminals in the consumer unit in order to avoid the line conductor becoming disconnected or damaged and making contact with the metal enclosure. e.g. clipping or clamping the tails, or installing in trunking and the use of a suitable cable-entry gland, In all cable entry arrangements, the enclosure shall not have sharp edges that could damage cables.
416.22. 416.22.1.
(b) entry point of the meter tails into the metal consumer unit must maintain the fire protection of the consumer unit so far as reasonably practicable. In essence, this means maintaining the requirement for the horizontal top surface of the enclosure to provide a degree of protection of at least IPXXD or IP4X and, elsewhere, IP2XC after installation in accordance with the manufacturer’s instructions as required by BS-EN-61439-3
522.8.1. 521.5.1.
(c) the meter tails also need to be protected to avoid any foreseeable damage and must enter a ferrous enclosure through the same entry point.
A non-combustible enclosure includes base, cover, door and any components, e.g. hinges, covers, screws and catches necessary to maintain fire containment, Devices and blanks are contained within the non-combustible enclosure and therefore, do not have to be manufactured in a non-combustible material e/g. steel, however, the use of non-combustible blanks is NOT precluded.
Where the consumer unit is to be located in an external non-habitable building, e.g. garage or shed, which is not in close proximity to a dwelling, consideration could be given to installing a consumer unit of non-ferrous construction, The term “ not in close proximity ” is always a moot point and the decision to install a non-ferrous enclosure must be supported by a documented risk assessment and must be appended to the Electrical Installation Certificate.