411.4 TN system
411.4.5 The characteristics of the protective devices (see Regulation 411.4.4) and the circuit impedances shall fulfil the following requirement:
Zs × Ia ≤ Uo ≤ Cmin
where: Zs is the impedance in ohms (Ω) of the fault loop comprising:
- the source
- the line conductor up to the point of the fault, and
- the protective conductor between the point of the fault and the source.
Ia is the current in amperes (A) causing the automatic operation of the protective device within the time specified in Table 41.1 of Regulation 411.3.2.2 or, as appropriate, Regulation 411.3.2.3.Where an RCD is used this current is the rated residual operating current providing disconnection in the time specified in Table 41.1 or Regulation 411.3.2.3.
Uo is the nominal a.c. rms or d.c. line voltage to Earth in volts (V).
Cmin ) is the minimum voltage factor to take account of voltage variations depending on time and place, changing of transformer taps and other considerations.
NOTE: For a low voltage supply given in accordance with the Electricity Safety, Quality and Continuity Regulations 2002 as amended,
Cmin ) is given the value 0.95.
NOTE : Where compliance with this regulation is provided by an RCD, the disconnection times in accordance with Table 41.1 relate to prospective residual fault currents significantly higher than the rated residual operating current of the RCD.
411.4.5 The characteristics of the protective devices (see Regulation 411.4.4) and the circuit impedances shall fulfil the following requirement:
Zs × Ia ≤ Uo ≤ Cmin
where: Zs is the impedance in ohms (Ω) of the fault loop comprising:
- the source
- the line conductor up to the point of the fault, and
- the protective conductor between the point of the fault and the source.
Ia is the current in amperes (A) causing the automatic operation of the protective device within the time specified in Table 41.1 of Regulation 411.3.2.2 or, as appropriate, Regulation 411.3.2.3.Where an RCD is used this current is the rated residual operating current providing disconnection in the time specified in Table 41.1 or Regulation 411.3.2.3.
Uo is the nominal a.c. rms or d.c. line voltage to Earth in volts (V).
Cmin ) is the minimum voltage factor to take account of voltage variations depending on time and place, changing of transformer taps and other considerations.
NOTE: For a low voltage supply given in accordance with the Electricity Safety, Quality and Continuity Regulations 2002 as amended,
Cmin ) is given the value 0.95.
NOTE : Where compliance with this regulation is provided by an RCD, the disconnection times in accordance with Table 41.1 relate to prospective residual fault currents significantly higher than the rated residual operating current of the RCD.