Buried on single phase max is 78 amps so no I wouldn't be fusing it to 80 amps. However is this a fixed load, one load, variable loads?
 
You wanted a gut feeling?

The volt drop gut says no. 80amps over 55meters? Nah.
You'd need bigger.
Don't worry about the price, that nice Mr Corbin seems to be prepared to pay for anything.
Thanks,think I would Vote bigger too,it’s political on site @ moment.
[automerge]1575819339[/automerge]
Buried on single phase max is 78 amps so no I wouldn't be fusing it to 80 amps. However is this a fixed load, one load, variable loads?
Variable loads
 
I'm a cheap skate so would try it with 10mm

That should keep the moles and worms nice and warm.

But look at the benefits, you could plant crops all along the cable route and get Avocado all year round!!
 
Thanks,think I would Vote bigger too,it’s political on site @ moment.
[automerge]1575819339[/automerge]

Variable loads
As there's a risk of overload then the cable size needs to be looked at again. At 80 amps design load your over the 5% threshold for volt drop. At a guess this is a distribution circuit and 25mm would be pushing it for volt drop when you take into account end of final circuits.
 

Reply to Real or unreal in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
918
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I seem to recall that written information for their approved installers listed an explicit requirement that it be wired and connected in all...
2
Replies
16
Views
1K
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
510

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top