Lots of missing information MateWould you fuse 16mm 3c Swa @ 80 amps.
Difficult to say when the details of the job are being withheld for some reason.Yea I know,just wanting a true gut answer really.
Lots of missing information Mate
Thanks,think I would Vote bigger too,it’s political on site @ moment.You wanted a gut feeling?
The volt drop gut says no. 80amps over 55meters? Nah.
You'd need bigger.
Don't worry about the price, that nice Mr Corbin seems to be prepared to pay for anything.
Variable loadsBuried on single phase max is 78 amps so no I wouldn't be fusing it to 80 amps. However is this a fixed load, one load, variable loads?
I'm a cheap skate so would try it with 10mm
As there's a risk of overload then the cable size needs to be looked at again. At 80 amps design load your over the 5% threshold for volt drop. At a guess this is a distribution circuit and 25mm would be pushing it for volt drop when you take into account end of final circuits.Thanks,think I would Vote bigger too,it’s political on site @ moment.
[automerge]1575819339[/automerge]
Variable loads