If there is a fault on one of the final circuits you would want the MCB to trip faster than the MCCB. A practical example of this I recall was one of the final circuits we installed the chippy put a nail through the cable now as we had a low ELI it took out the RCBO as well as the existing 50A MCB protecting this D.B. bad discrimination ( sorry selectivity new word)
Trip faster? Does the MCCB not have to trip within 0.4s ?
 
If there is a fault on one of the final circuits you would want the MCB to trip faster than the MCCB. A practical example of this I recall was one of the final circuits we installed the chippy put a nail through the cable now as we had a low ELI it took out the RCBO as well as the existing 50A MCB protecting this D.B. bad discrimination ( sorry selectivity new word)
In that situation you would wanna substitute the 50A MCB for a type C or type D MCB?
 
0.4 sec under 32A and 5 sec over 32A
In the situation you describe surly a 50A type c or type D MCB would be the solution?
There's a small matter of short circuit capacity rating involved, here, mate.
 
Last edited:
My question would be, say if you're PFC and PSSC are less then 18,000 Amps, why would you use a MCCB over an MCB on a main DB supplying a sub DB?
 
Your tripping characteristics are completely different from your standard circuit breakers hence manufacturers data should be sought as have you never noticed how no maximum zs values are published in bs7671 regarding mccb’s?
They can have both the magnetic and overload characteristics set , depending on the application they are being used for and what they intended to supply and protect.
 
I’ve had to delete loads of posts....It took me ages :(. I’ve had to delete posts that were just silly/off topic, other posts that quoted such posts and then posts which would no longer make sense due to previously deleted posts. Please play nice and keep the thread on track. Cheers guys and girls.
 
Okay Gigsy, from afar and not seeing the job first hand this is probably what I would do. Shorten the swa supply cable and make it off into a 63A isolator, from here take some 6181Y tails to the meter that way you have no unenclosed conductors. Those protective devices at the main board with the orange toggles are BS3871 Type 3, cant make out the other but it is not compatible with the enclosure and the cover has probably been cut away to fit it.
 
Okay Gigsy, from afar and not seeing the job first hand this is probably what I would do. Shorten the swa supply cable and make it off into a 63A isolator, from here take some 6181Y tails to the meter that way you have no unenclosed conductors. Those protective devices at the main board with the orange toggles are BS3871 Type 3, cant make out the other but it is not compatible with the enclosure and the cover has probably been cut away to fit it.
Thank you :)
I will not use rear entry again. From now on 4 inch metal trunking top and bottom into glands and make off the SWA into the board. And I would insist on the customer purchasing the meter designed to go in the board.
 

Reply to Rear entry three phase board in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

That won't solve the problem, you have a TNCS supply with a Ze which has gone out of spec for an unknown reason. You need to get the DNO or...
Replies
24
Views
4K
davesparks
D
  • Question
Agree with Dave disconnect unused Phases on the outgoing side of the isolator. No reason to replace mcbs with single pole, unless you need room...
Replies
2
Views
1K
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2
Replies
47
Views
4K
We use hager all the time very neat with the built in SPD as pc1966 says you can get them with SPD and main switch fitted for about £700
Replies
5
Views
2K
  • Question
There CT stands for current transformer. Basically for meters up to around 100A they are usually directly connected, i.e. the current passes...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks