within a building supplied my a PME system it’s not possible to main bond the extraneous conductive parts effectively back to the origin.

Resolution instead of changing to a TT system remove the extraneous conductive parts.

Water pipe: this comes out the ground so change this to plastic and put a stop cock on the plastic section then box it off.

Soil stack: simply just box it in.

Can anyone see anything wrong with that? Saves allot of agg
 
Unless I have missed it I assume this relates to your other threads, so is this can install you carried out or an EICR you carried out on an existing installation.
 
Hi Chris,
This is your 4th thread related to the same issue. Unless there are more I don't know about. You could have kept all the different queries related to it in the one thread.

Just TT the Installation as your assessor has requested.

That's if your customer is now allowing access.

Good luck Pete

P.S. I am now out.
 
Surely it would be quicker and easier and cheaper to just TT it than bother with changing pipework and carpentry? Would boxing in the soil stack comply anyway?
This was actually a question I was asked in my assessment for stroma and the answer was to TT the installation.....
 

Reply to Removal of extraneous conductive part in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top