Just been sorting out a right mess during a house renovation and tests on newly installed ring final are r1 0.35
rn 0.35 & r2 was expecting around 0.58 but had consistently 0.00 Ohms.
MFT was zeroed again from scratch and was still giving a zero resistance reading
Almost all cable is new and IR tests all perfect. Any ideas ? Thanks
 
Sounds like the earth has shorted on the beginning run of the cable as you had 0.35 on rn/r1 must be the earth ring is so short it reads 0.00 does your tester go to three figures? Have you tested at the middle socket? r2? end to end that would indicate if that was the case.
 
Back there Friday to finish up so I'll check more extensively then, closest socket to board 0.09 ohms which is very close to the board. Is a really small ring too. Cheers
Tested R1 +R2, and R1 to RN too etc to check all. Yes tester goes to 3 figures is Fluke 1653B
 
What position are you testing the ring from the consumer unit or socket ? I have had it in the past where had small ring and the dampness of plaster damp wall between the metal k.o. boxes have given a lower continuity reading than I should of had but not that low.
 
What position are you testing the ring from the consumer unit or socket ? I have had it in the past where had small ring and the dampness of plaster damp wall between the metal k.o. boxes have given a lower continuity reading than I should of had but not that low.
Tested at each socket on newly rewired small ring, as said expected around 0.58 and got 0.00! After 0.35 each on L's & N's cross connected.
 
Maybe cables have been jointed somewhere but cpcs have been connected together in one connection rather than connected in 2 separate connections.
But 0.00 ohms suggests that the cpc ends are crossed in the db with another circuit
 

Reply to Renovated house low r2 readings ! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
744
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top