Soulsurfer

-
Arms
Joined
Feb 21, 2013
Messages
623
Reaction score
163
Location
Channel Islands
Just been sorting out a right mess during a house renovation and tests on newly installed ring final are r1 0.35
rn 0.35 & r2 was expecting around 0.58 but had consistently 0.00 Ohms.
MFT was zeroed again from scratch and was still giving a zero resistance reading
Almost all cable is new and IR tests all perfect. Any ideas ? Thanks
 
[ElectriciansForums.net] Renovated house low r2 readings !
 
I'd disconnect the 13A sockets each side of the CU and then measure R2 end to end from each socket. One test round the ring. The other test to and from the CU. With the CU CPCs for the RFC still disconnected at the CU.
That should give a sensible remainder of ring R2 and isolate the issue in the cables going to and from the CU.
You may need a wander lead of course.
 
I'd disconnect the 13A sockets each side of the CU and then measure R2 end to end from each socket. One test round the ring. The other test to and from the CU. With the CU CPCs for the RFC still disconnected at the CU.
That should give a sensible remainder of ring R2 and isolate the issue in the cables going to and from the CU.
You may need a wander lead of course.

Ehhh? Soulsurfer has found the 'fault' :)
 
Carrying out tests on new builds we have been carrying out, get first test cert over from sparks on site LL & NN look good earth way down low, then remembered metal walls caddy straps light circuits ect.
Few days later same site different sparks phone call same as above been checking everything he tells me I mention parallel paths & phone goes silent the penny drops oh S...t of course.
Not quite as low as fist post but quite low.
See it on the test sheet kitchen all good block walls, tin in the up & downstairs rest of house so 2 rings affected.
 
Extended most of the circuits from old 3036 board to new board and used a box with din top hat mounted creating a huge earth bus bar in effect :rolleyes: felt a right prat

SS, I read this post all the way through thinking what could it be, and you led us on a right merry dance mate! Prat is correct! But we all can't see the woods for the trees every now and then! My initial thought was both legs going through one back box near the CU, with the CPCs joined there, as I have seen that sort of thing before. Well done for, ahem, finding it! ;)
 
Extended most of the circuits from old 3036 board to new board and used a box with din top hat mounted creating a huge earth bus bar in effect :rolleyes: felt a right prat
Maybe you could add this to the never have i ever thred , we have all done some silly things in the past , at least what you have done is not dangerous and you found what was coursing your low reading before you stripped the installation down back to its component parts . :)
 

Reply to Renovated house low r2 readings ! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
744
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top