Just been sorting out a right mess during a house renovation and tests on newly installed ring final are r1 0.35
rn 0.35 & r2 was expecting around 0.58 but had consistently 0.00 Ohms.
MFT was zeroed again from scratch and was still giving a zero resistance reading
Almost all cable is new and IR tests all perfect. Any ideas ? Thanks
 
Wot about doing the r1+r2 test on each leg, like when your trying to find a break in a ring? Break the ring at the furthest socket, then test each leg? Just a suggestion, might be a pants idea?
 
I must admit I'm a little puzzled by you opening sentence ... "sorting out a right mess" - so are you testing an installation you didn't do?

If this new ring is your work, it should be a formality to resolve the issue.

Existing was a bad spider jointed mess have taken out almost all cables except one old leg which I couldn't get out so re-used & all rest is new cable.
 

Reply to Renovated house low r2 readings ! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top