If your replacing a shower like for like power wise, are you under any obligation to supply rcd for this? As no alteration has been made to the circuit and no change of opd has been done?
 
Had this with niceic before. Manufacturers instruction supersede 7671 . No more to be said. If you do not install to manufactures instructions it will not comply as they will never instruct you to do anything against the regs but they may ask you to go over and above the minimum standard.

I assume if manufacturers instructions supersede BS7671 then this would have to be listed as a departure from the regs on any certificate

This could also be interesting in a court if the manufacturers instructions due to errors did not fully meet the requirements of the regs and an incident occurred
 
I assume if manufacturers instructions supersede BS7671 then this would have to be listed as a departure from the regs on any certificate

This could also be interesting in a court if the manufacturers instructions due to errors did not fully meet the requirements of the regs and an incident occurred

my driving licence doesn't tell me not to run people over, but it doesn't mean I can
 
Here are some excerpts from manufacturers' instructions for fiting electric showers:

Triton:
The following notes are for guidance only:
5.1 A 30mA residual current device (RCD) must
be installed in all UK electric and pumped
shower circuits. This may be part of the
consumer unit or a separate unit.


Gainsborough:
IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENT DEVICE (RCD) SHOULD BE INSTALLED IN ALL
UK 230-240V ELECTRIC SHOWERS. THIS MAY BE PART OF A CONSUMER UNIT OR A SEPARATE UNIT.

Mira:
It is strongly recommended that a 30 mA Residual Current Device (RCD) is
included in the electrical circuit. This may be part of the consumer unit or a separate unit.

Aqualisa:
IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENTDEVICE (RCD) SHOULD BE INSTALLED IN ALL UK 230-240V ELECTRIC
SHOWERS AND PUMPED CIRCUITS. THIS MAY BE PART OF A CONSUMER
UNIT OR A SEPERATE UNIT.

Creda and MX don't mention anything about RCDs whatsoever.

Who are these manufacturers' that state an RCD must be fitted in their instructions?
 
Last edited by a moderator:
Instructions for Triton:
The following notes are for guidance only:
5.1 A 30mA residual current device (RCD) must
be installed in all UK electric and pumped
shower circuits. This may be part of the
consumer unit or a separate unit.


Instructions for Gainsborough:IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENT DEVICE (RCD) SHOULD BE INSTALLED IN ALL
UK 230-240V ELECTRIC SHOWERS. THIS MAY BE PART OF A CONSUMER UNIT OR A SEPARATE UNIT.

Instructions for Mira:It is strongly recommended that a 30 mA Residual Current Device (RCD) is
included in the electrical circuit. This may be part of the consumer unit or a separate unit.

Instructions for Aqualisa:
IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENTDEVICE (RCD) SHOULD BE INSTALLED IN ALL UK 230-240V ELECTRIC
SHOWERS AND PUMPED CIRCUITS. THIS MAY BE PART OF A CONSUMER
UNIT OR A SEPERATE UNIT.

Creda and MX don't mention anything about RCDs.







That's my point spin. Your arguing against yourself. I said yes you said no

- - - Updated - - -

Instructions for Triton:
The following notes are for guidance only:
5.1 A 30mA residual current device (RCD) must
be installed in all UK electric and pumped
shower circuits. This may be part of the
consumer unit or a separate unit.


Instructions for Gainsborough:IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENT DEVICE (RCD) SHOULD BE INSTALLED IN ALL
UK 230-240V ELECTRIC SHOWERS. THIS MAY BE PART OF A CONSUMER UNIT OR A SEPARATE UNIT.

Instructions for Mira:It is strongly recommended that a 30 mA Residual Current Device (RCD) is
included in the electrical circuit. This may be part of the consumer unit or a separate unit.

Instructions for Aqualisa:
IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENTDEVICE (RCD) SHOULD BE INSTALLED IN ALL UK 230-240V ELECTRIC
SHOWERS AND PUMPED CIRCUITS. THIS MAY BE PART OF A CONSUMER
UNIT OR A SEPERATE UNIT.

Creda and MX don't mention anything about RCDs.







That's my point spin. Your arguing against yourself. I said yes you said no
 
Instructions for Triton:
The following notes are for guidance only:
5.1 A 30mA residual current device (RCD) must
be installed in all UK electric and pumped
shower circuits. This may be part of the
consumer unit or a separate unit.


Instructions for Gainsborough:IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENT DEVICE (RCD) SHOULD BE INSTALLED IN ALL
UK 230-240V ELECTRIC SHOWERS. THIS MAY BE PART OF A CONSUMER UNIT OR A SEPARATE UNIT.

Instructions for Mira:It is strongly recommended that a 30 mA Residual Current Device (RCD) is
included in the electrical circuit. This may be part of the consumer unit or a separate unit.

Instructions for Aqualisa:
IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENTDEVICE (RCD) SHOULD BE INSTALLED IN ALL UK 230-240V ELECTRIC
SHOWERS AND PUMPED CIRCUITS. THIS MAY BE PART OF A CONSUMER
UNIT OR A SEPERATE UNIT.

Creda and MX don't mention anything about RCDs.







That's my point your arguing against yourself spin. I said yes you said no
 

Reply to Replacement shower in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
792
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
818

Similar threads

M
  • Article
Tiling on Universal Shower Bases Hi there - I’m hoping to get some advice. I’m a builder, based in Melbourne, Australia. I’ve recently done a...
Replies
0
Views
136
Melbourne Builder
M
J
  • Article
Traymate Shower tray Hi guys, This is my first post so apologies if this isn't the right section for the post. I'm a qualified plumbing and...
Replies
0
Views
150
Jeefa
J

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top