keniff

-
Joined
Aug 7, 2010
Messages
885
Reaction score
105
Location
east sussex
If your replacing a shower like for like power wise, are you under any obligation to supply rcd for this? As no alteration has been made to the circuit and no change of opd has been done?
 
This Q & A is taen from the ESC web site:-

"Q2.10If I replace an existing electric shower, do I now have to provide RCD protection for it?

No, unless RCD protection is required by the manufacturer’s installation instructions, or a new circuit is required (to provide for increased load, for example).
Regulation number(s)

  • 134.1.1
  • 510.3"


2. Alterations and additions in domestic and similar premises : Electrical Safety Council

Q 2.10


 
the correct procedure is to connect up the new shower to the leccy first, then get the plumber to do the water bit. only after the plumber has been electrocuted, should you return to fit the RCD.
 
Spinlondon spin on this lol :prrr:

[ElectriciansForums.net] Replacement shower
 
Spinlondon spin on this lol :prrr:

Just for interest I contacted Mira this morning asking them about their views on RCD protection with showers. I used the extract Spin (I think) posted from a Mira product guide. It seems that their view is that an RCD must be used

Read more: http://www.electriciansforums.net/e...69843-replacement-shower-5.html#ixzz2H1ME8P4L

- - - Updated - - -

Thanks richy3333 for previous post

This is the latest offering from Mira:
Electrical (checklist in detail)
1.
In a domestic installation, the rating of the electricity supplier's fuse and the consumer unit must be adequate for the additional demand. All Mira Sport electric showers are high power units, therefore it is essential to contact your electricity supplier to ensure that the supply is adequate for the product. Voltage drop due to local heavy demand will reduce the shower's performance.
2.
The Mira Sport must be earthed by connecting the supply-cable earth conductor to the earth terminal.
Supplementary bonding:
Within the bathroom or shower room, all accessible conductive parts of electrical equipment and extraneous conductive parts (metal parts) that are likely to introduce earth potential, must be electrically bonded to earth using a minimum cable size of 4.0 mm2 if the cable is not mechanically protected, (2.5 mm2 if mechanically protected).
3.
Supply cable - see opposite.
4. As a guide only
, and in accordance with BS 7671 we recommend close circuit protection: i.e. 7.5 kW & 9.0 kW = 40 Amp, 9.8 kW = 45 Amp
5.
A 30 mA Residual Current Device (RCD) MUST be included in the electrical circuit (BS7671). This may be part of the consumer unit or a separate unit.
A separate, permanently connected supply is taken from the consumer unit to the appliance through a double-pole switch, which has at least 3 mm contact separation. The switch can be a ceiling mounted pullcord type within the shower room or a wall mounted switch in an adjacent room.
6. DO NOT
twist the individual cable cores of either the live or neutral conductors, as this will prevent them from entering the terminal block.
7. DO NOT
exert strain on the terminal block. Ensure that the electrical connections are tightly screwed down.
8. DO NOT
turn on the electrical supply until the plumbing has been completed.

You may think that the sentance "A 30 mA Residual Current Device (RCD) MUST be included in the electrical circuit (BS7671)." is an instruction for you to fit an RCD.
It's not.
It's rather poorly informing you that BS7671 requires the circuit be provided with 30mA RCD protection.
Just the same as No. 2 is incorrectly informing you that Supplementary bonding is required, and how to provide it.
Would you or anyone else fit supplementary bonding if it were not required by BS7671, just because the Mira installation electric shower instructions tell you to?
 
the correct procedure is to connect up the new shower to the leccy first, then get the plumber to do the water bit. only after the plumber has been electrocuted, should you return to fit the RCD.

Thanks Tel' that made me chuckle after a stressful afternoon with a plumber :D
 

Reply to Replacement shower in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
795
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
827

Similar threads

M
  • Article
Tiling on Universal Shower Bases Hi there - I’m hoping to get some advice. I’m a builder, based in Melbourne, Australia. I’ve recently done a...
Replies
0
Views
137
Melbourne Builder
M
J
  • Article
Traymate Shower tray Hi guys, This is my first post so apologies if this isn't the right section for the post. I'm a qualified plumbing and...
Replies
0
Views
150
Jeefa
J

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top