Got a job coming up replacing 3 old storage heaters with panel heaters. Customer is coming off E7. Had a look today and was expecting the usual 3 x 16A MCBs, but found that all 3 heaters are on a single 6mm^2 circuit. There is an 850W unit, a 2.55kW and a 3.4kW one sitting on a 32A MCB. I have never seen storage heaters installed like this. If nothing else, loads greater than 2kW should be on dedicated circuits. The loading of the panel heaters is going to be similar, 29A ish, although the load won't as punishing due to cycling on and off and not all being on continuously for hours. I haven't decided if I am happy to do the change with this circuit as it is. Mind you I haven't tested the cable yet either. Any advice or thoughts would be appreciated.