I suppose the best compromise Ive seen is the fuse cover back removed so at least with plug in MCB's it can still be fitted, thus covering these exposed parts.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Rewirable fuses and the old wylex boards in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
My first house had two 8 way Wylex boards that I fitted (they were the best on the market at the time). When the MCB’s became available I fitted them. Both boards had a separate 500mA RCCB.
We had to work with what was on the market at the time. I will say that in over 20+ years I never had a fuse blow or MCB trip due a fault. Just to add to the confusion there were two sub boards fed from the main boards.
The one in my dark room was a Telemecanique board with a 10mA RCD.
Again not many houses could boast a 110V ring main and 100V DC radials.
absolutely bizarre,, AS an Electrician If your fitting Blanks to a board where they just pop out then you are leaving a potential risk. FIT one that doesnt just pop out.. It would be your arse on the line when something happens..
(copy from a previous post i made)
Dont know If people have looked closely at the Wylex type of rewirble fuse boards? Without the screw on cover over the fuses there is exposed live parts on show under and on top of the fuse carrier... about 2- 3mm
If the fuse cover is missing (not the carrier but the 4/6 way cover) and the fuses can be seen, this goes against reg 416.2.2
If the cover is there and can be undone without a tool then again I think this goes against the same reg..
look at the top of this board,,
Redirect Notice
Looking at section 416 it describes basic protection as being a minimum of IP2X or IPXXB, which to my understanding is the equivalent diameter of a small finger (12mm). So the front surface (vertical) of a Wylex board without its fuse cover would still comply. The top surface is another matter where the restrictions in diameter are more appropriate and that being IP4X or IPXXD.
Here's some pics I found whilst on the net
What code would you put on this one?
View attachment 9932
or what about this !
View attachment 9933
Im sure people are missing my point..
you come across this board Redirect Notice
high up in a garage, not so bad.
you come across this board under the stairs at low level! in my eyes this goes against regs
if the screw on cover was there no problem at all totally fine no code needed..
I under stand reg 416.2.1 but after that it says
416.2.2 A horizontal top surface of a barrier or enclosure which is READILY ACCESSIBLE shall provide a degree of protection of at least IPXXD or IP4X (less than 1mm)
This cant just be ignored can it?
Too me the red white and blue fuse carriers with the holes in as shown in the picture are horizontal top surface?? again if im making a mistake here please point me in the right direction