Went to a job yesturday.
6.6kw 4 ring hob and 4.2kw cooker were both supplied on same 6mm on 32a breaker!! Both still using the 1mm flex pre-wired to them.
Running in another 6mm was not really a option as tenant didnt want trunking!
So kept the original 6mm and put that into supply side of 45a 2g cooker switch and a new bit of 6mm from load side to ccu, then ugraded the 1mm pre-wire to a 6mm from ccu to the hob.
Then as the 1.5mm pre-wired flex couldnt be disconnected from the cooker and there was no way a 6mm would even get in the small hole of the cooker, i left the cooker on a 13a plug and spurred off of ring with a 13a sw fused spur above work top and a single socket below for cooker to plug into to.
I know the cooker can pull u to 18a, but with diversity taken into account all the above is ok right?
Cheers