stuey gonna do me a fav n phone IET with your calculations so they can rewrite the regs Id love to hear their reaction to a 40a ring on 1.5

Take a look at table 4D2A (p276) of bs7671.

Using Ref method C 1.5mm will safely pull 19.5A....

If you ring it, you effectively double it's CCC.

So, A ring circuit using 1.5mm protected by a 32A MCB is more than safe ( Ib<In<It ) (but does it comply?)
 
I cannot find any regs stating 1.5 is unacceptable for a RF. Not good practice imo, but can anyone show me the regs to show it dosent comply?

Even with a 32A pull voltage drop is still <5% too.

Still shoddy though.

OP, why would you even consider altering the circuit ? Just pull some shiny new copper !
 
Had a look at said table but does not say wired as a ring. Sockets can be wired in 1.5mm but only spurred off a ring through a fuse spur and wired in a radial not a ring, does not comply.
 
Take a look at table 4D2A (p276) of bs7671.

Using Ref method C 1.5mm will safely pull 19.5A....

If you ring it, you effectively double it's CCC. No you dont, not in CCC aspect.

So, A ring circuit using 1.5mm protected by a 32A MCB is more than safe ( Ib<In<It)Sorry mate but that bit is nonsense. (but does it comply?)


Wrong table Stuey.....flat T+E is table 4D5, P282.

Applying the correction factors a 1.5mm T+E at it's best (not clipped direct as it wont be) will just about take 16A.

In theory you can have a ring circuit of any size.....caravan parks for example, and the rule of thumb for sizing a cable to an OCPD is to mutiply the OCPD by 0.67 to give you the minimum CCC of the cable to be installed as the ring, i.e - 32 x 0.67 = 21.44A, well above the max for a 1.5.

This is how I arrived at 20A in my previous post, 20 x 0.67 = 13.4A, below the max for a 1.5.:) I personaly still would not do that though, and would ideally rip it all out and start again.
 
Gulp........... After reading all that im lost what to do now..............

What is the best action for it to be safe for a couple of weeks or so

1: Spilt the ring into 2 radials and put on 16amp breakers ?
2: Keep the ring and put on a 20 amp breaker ?

Just dont want a fire .................
2:
 
As a ring circuit, it is at the best unconventional, at worst it is not permitted
The Brb may not state that,but it is not a standard circuit

The discussions over the current carrying capacity has not mentioned the cpc
This being 1.0mm would definitely make me decide to split the ring and 16amp the radials
You will need then to split the circuit where loading and circuit readings allow
 
As a ring circuit, it is at the best unconventional, at worst it is not permitted
The Brb may not state that,but it is not a standard circuit

The discussions over the current carrying capacity has not mentioned the cpc
This being 1.0mm would definitely make me decide to split the ring and 16amp the radials
You will need then to split the circuit where loading and circuit readings allow


But as a ring it has 2mm of cpc.... :) Pah, boring myself now. :)

Personally I would not touch the circuit until the customer agrees to rewiring it.
 

Reply to Ring Circuiot in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
564
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
937

Similar threads

Outside socket… ok. But you say the fcu for boiler is beside the outside socket… is the boiler outside too? FCU’s have an IN and an OUT… the OUT...
Replies
2
Views
231
Yep! Edit button was disabled by the time I seen it. Hopefully the 15m/15m clarified what I intended 😀
2 3
Replies
36
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top