OP
GStueyXR
stuey gonna do me a fav n phone IET with your calculations so they can rewrite the regs Id love to hear their reaction to a 40a ring on 1.5
Take a look at table 4D2A (p276) of bs7671.
Using Ref method C 1.5mm will safely pull 19.5A....
If you ring it, you effectively double it's CCC.
So, A ring circuit using 1.5mm protected by a 32A MCB is more than safe ( Ib<In<It ) (but does it comply?)