ring design and voltage drop
Sounds like your computer thinks it is a mobile phone, so the forum is sending you to the mobile site or vice versa.
Unfortunately I do not know how the forum does that (client or server) so can't help.
Usual things of clearing caches, directly typing the forum address in the address bar not using links/favorites. but you have probably tried all that. Make sure there are no spurious m's in the web address you go to.
Good luck
Ive used both ohms law R = V / I and used the values of mohms per meter out of table 4D5 in BS 7671.
From the OSG 2.5 T&E has a resistance of 0.01951 ohms per meter, so R = 0.01951 times m (meters) that is
R = 0.01951 * m
Ive taken V as volt drop at 11.5V and I as 32A, the rating of the PD, giving:
0.01951 * m = 11.5 / 32 ohms law
or m = (11.5 / 32)/0.0195 = 18.43m ??
Using the mV/A/m from table 4D5 of BS 7671, we have a value of 18mV, therefore
(18*32*m)/1000 = 11.5V
or m = 19.96m ??
Ive got this all wrong i know i = p/u. Think my perceptions of how a RFC handles voltage and current is off the scale!! But now ive had a thought from a post earlier.
Is from jamesbrownlive's post above, pg2, and how you both mention about dividing by 4. It would seem logical that when considering a RFC's construction, we have to consider that as a ring the CSA is doubled and the length effectivly halved, which would reduce the resistance to 1/4 of its standard value of 0.0195 ohms per m, in this case that would become 0.004875 ohms per m. Recalculating we have:
0.004875 * m = 11.5 / 32
m = 73.7m
which now seems ample length of cable to construct an A1 ring
What you think?
I think your not far off, you need to make a further consideration to load distribution and conductor temperature and your there.
Regards Chris
I use an (Ib) of 26A when calculating for an A1 RFC which would gives a maximum length of 98M.
It can be engineered further but I prefer to err on the side of caution with 26A and (Ct) of 1.
Hi spinlondon, i never been taught to use diversity with cable selection. That doing so is is a definite no no. Diversity is applied to maximum demand to give a practical/realistic expectation of the current being drawn off he supply and hence through the service fuse at any one time.
Cheers chris. Im trying to get my head around load distribution and the calculations.
Get what you say about conductor temperature.
I've done the calculation without any correction and method C to keep things as simple as possible
Consider then a RFC with 10 socket-outlets.
What CSA of cable would your method indicate, and what rating of CPD would be required?
That is how I work out the length and volt drop in a Ring.
Length
2.5mm T&E ring.
1 conductor 2.5mm CSA @ 7.41mohm/m
1 conductor 1.5mm CSA @ 12.10mohm/m
{from page 166 OSG}
so if you have a measured value of say
r1 @ 0.58/7.41 x 1000 = 78.27m
rn @ 0.58/7.41 x 1000 = 78.27m
r2 @ 0.96/12.10 x 1000 = 79.33m
Volt Drop
Divide the length by 4 = 19.57 x 18 x 26/ 1000 = 9.16v
Bs 7671 pg 258, 6.1 correction for operating temp.
This calculation give you a ct of .923, x 9.16 = 8.45v
or
4 x 8.45v x 1000/26/18 = 72.22 / .923 = 78.24m
It assumes 20 amp at the furthest point and 12 amp distributed evenly around the ring so,
average = (32 + 20)/2 = 26 which is the value that Lenny posted.
Hi lenny, im with i = p/u. Can we see you full calc
Cheers
Ok, VD will limit the length of your RFC before any other factor. So if we use our max permitted VD of 11.5V in our calc for finding the max permissable length we 'should' arrive at a value within the 5% tolerance.
So (4 x 11.5 x 1000)/(Ib x mV/A/M x Ct) = max permissable length.
= (4 x 11.5 1000)/(26 x 18 x 1) = 98.29M.
As I said it can be engineered further to give a longer length but I personally use the above.
Cheers for your help spinlondon, things are getting clearer. Have always taken appendix 15 as is, with no explanation of the design behind these circuits. Radial are fine, the ring threw me, so thanks for your help in this matter
esc
esc,
i=p/u,
TrueNAS JBOD Storage Server