If it's been tampered with assume the worst and 100% test. As onions1066 says while your at the db just quickly test for continuity with the other circuits, you'll be surprised what you find. "Heinz Canned Worms"
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Ring Final Circuit Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
That about sums it up, yeah!
We've only been in the house a year and finding all sorts...
Took down a door standard a few months ago and a mass of wiring came down (grouped), and judging by the shoddy connectors and absence of sheathing on the cpc it would clearly suggest someone had be screwing around with it! .. So much for rating factors when people just pull things apart and shove them together anyway!! :-/
this fault has "diy upgrades" written all over it lol.
walk around with your Loop meter find the higest reading, remove socket, find broken conection, reconect it,, jobs done
I'll tell you how i do it, without the hassle of dragging wander leads all over the gaff.
Remove all the plugs from the sockets in that circuit. connect one leg only of the offending component of the ring, perhaps an earth in your case and then go round with a typical three neon socket tester and find out at which point you go from earth fault to a good reading. Then connect the other end and do the same in the opposite direction - you will narrow down the fault in no time.
If the fault is within an FCU on the ring main, you will also be able to narrow this down too.
Then do the same for your line circuit.
I have used this method loads of time and it is much quicker than pulling the wander lead around.
this fault has "diy upgrades" written all over it lol.
Reply to Ring Final Circuit Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net