If you explain (if they should ask, unlikely) that you felt that the CPC resistance result was low due to parallel paths from the existing installation, you made investigations and found one partial resolution.Just to update, I disconnected the earth to the boiler and the reading went straight up to 0.65 ohms! result, but still not the 1 ohm(ish) i was looking for so maybe another parallel path somewhere. I took off a few other earths but it stayed the same. I dont know if the Elecsa assessor is going to expect me to get a higher reading than that or maybe just explain why i think its that low? I dont want to get too side tracked by this one thing i know there is a lot of other things i need to worry about too!!!
Michael
i think I have lost the plot on this one
You have changed a consumer unit
You have verified a ring final has end to end continuity
You have established Zs on each outlet is within limits
You have spent days looking for and worrying about probable parallel earth paths that are making cpc readings better than expected
If this was a new installation and this were initial verification, then all well and good,but this is a consumer unit change,the circuit has been established as safe for reconnection,that is what you are expected to ascertain
You have the probable reasons why the readings vary and could answer the assessors questions if required
Why rip an "existing" installation to bits to find what can be explained by installation variations that are usual and often present
Had my assessment yesterday and passed with an A. It was very relaxed and was mostly just chatting about Elecsa. I referred to the electricians guide to the building regs a few times when asked questions. I had a few blank moments when i was asked the most simple of questions! I done a Ze test, PFC, PSCC, RCD test, a Zs on one socket and was asked to do an end to end on the ring circuit i had a dodgy reading on. I explained the situation straight away and he said the fact i spotted it and new it was a parallel path was fine. (so big thanks to all the advice given on here about it) After 6 weeks of build up and stressing i feel a bit deflated, it really is nothing to worry about in the slightest the Elecsa guys are there to advise and guide you more than try and catch you out. I didn't even get any non conformaties or recommendations which i was surprised about. He said i should still look for any parallel paths just for my own peace of mind and to help me when i come across it again which I probably will on the next job! Thanks for all the advice once again. Now i need to start earning some money!
Michael