Another straight forward job today has turned out to be a right mess once again so I thought I'd get some thoughts on the following before I start !
So an old MK LN59 board, feed to garage sockets on a single 2.5mm t&e from a 15A mcb and also spurred to feed a boiler on S plan,
Next ring final on a 30A feeding upstairs sockets as usual but on cover removal I found a 4mm t&e spurred from same 30A mcb and feeding opposite side of garage to sockets all on the 4mm then at the end spurred from last socket with 2.5mm t&e to feed new water cylinder via a DP switch !
Obviously I'm not happy with the 4mm being spurred as an extra circuit from a separate circuit pd but surely the immersion being spurred from sockets is rough too ?
Never seen anything like that before !
So an old MK LN59 board, feed to garage sockets on a single 2.5mm t&e from a 15A mcb and also spurred to feed a boiler on S plan,
Next ring final on a 30A feeding upstairs sockets as usual but on cover removal I found a 4mm t&e spurred from same 30A mcb and feeding opposite side of garage to sockets all on the 4mm then at the end spurred from last socket with 2.5mm t&e to feed new water cylinder via a DP switch !
Obviously I'm not happy with the 4mm being spurred as an extra circuit from a separate circuit pd but surely the immersion being spurred from sockets is rough too ?
Never seen anything like that before !