Ring main r1+r2 reading really low - 0.01? | Page 2 | on ElectriciansForums
Discuss Ring main r1+r2 reading really low - 0.01? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Are you testing you R1R2 at the consumer unit or at a socket?
You sure you havent got you 2 cpcs touching if test at the CU and they’re not fully sleeved or seperated?
had a similar scenario a while back when replacing a part of a damaged RFC, the electrician who did the original install had twisted the 2 cpc's together in the back of the consumer unit, they were then separated out and sleeved to the earth bar in the CU, so at first glance appeared separate, it caused a little confusion at first, as soon as i untwisted the wires so they were not touching, I got sensible results.
Yep I know it is funny I only mentioned it because I had the pleasure of seeing a mock new 2391-51/52 mutiple choice question paper recently, a similar question was written on it ;)
Strictly text book, taking you as far as the design scope of the course (not allowing diversity for maximum load from the centre of the ring)
Assuming a ridiculous scenario of the ring running at full load (32amps ×R1+Rn) the R1+Rn would already fail the maximum permissible 5% volt drop, and that's before you add the correction factor for the circuit running at 70°c. (a multiplier of 1.2 to R1+Rn)
Really just mentioned it for the trainees as I thought it was a bit of a silly question.
Reply to Ring main r1+r2 reading really low - 0.01? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...