Are you testing you R1R2 at the consumer unit or at a socket?

You sure you havent got you 2 cpcs touching if test at the CU and they’re not fully sleeved or seperated?
 
had a similar scenario a while back when replacing a part of a damaged RFC, the electrician who did the original install had twisted the 2 cpc's together in the back of the consumer unit, they were then separated out and sleeved to the earth bar in the CU, so at first glance appeared separate, it caused a little confusion at first, as soon as i untwisted the wires so they were not touching, I got sensible results.
 
Yep I know it is funny I only mentioned it because I had the pleasure of seeing a mock new 2391-51/52 mutiple choice question paper recently, a similar question was written on it ;)
Strictly text book, taking you as far as the design scope of the course (not allowing diversity for maximum load from the centre of the ring)
Assuming a ridiculous scenario of the ring running at full load (32amps ×R1+Rn) the R1+Rn would already fail the maximum permissible 5% volt drop, and that's before you add the correction factor for the circuit running at 70°c. (a multiplier of 1.2 to R1+Rn)

Really just mentioned it for the trainees as I thought it was a bit of a silly question.
 
Last edited:

Reply to Ring main r1+r2 reading really low - 0.01? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
546
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
990
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
931
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
421

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top