I'm not saying I would do this because I wouldn't install like this, but I am going to play devils advocate.
Which regulations does such an arrangement breach?
And how would two ring final circuits installed in accordance with the regulations connected to the same 32A MCB be dangerous?
As I say I wouldn't do it, except as a temporary measure to restore supply, so I'm just curious about the thought process behind the statements.
In all honesty I cannot see anything in Bs7671 that this would contravene other than good workmanship. If it originates from one MCB it is a single circuit. Despite what has been said about it overloading there is no reason to assume it would be. A single ring with 10 double sockets could have 20 3kw heaters plugged into it.
Very poor practice though and it needs altering on that basis.
edit. Post crossed with Sparkychick who has reached the same conclusion.
@SparkyChick
I have been having similar thoughts,
I don't think its right, and its not something I would install as new.
however I have just been browsing the book, and nothing is jumping out to say I couldn't do it if I wanted to.
I think we can mostly all agree that it is certainly not best practice but if someone could point me to a reg number it would make me feel better.
It may not disagree with any regulations, but SC you surely can see the apparent dangers of applying such a circuit.
[automerge]1588091274[/automerge]
@SparkyChick
Don't think you need a reg number SC look up the description of a circuit.
I fully agree that this is incorrect and should not have been done.
But having said that what are the apparent dangers? I don't see any particular danger attributable to this.
The definition of a circuit is based around everything that is connected to a single way in a distribution board, so this would still count as one circuit, although it is nom-standard.
[automerge]1588091644[/automerge]
You could put more than one radial on a MCB but its not good practice.
You can have two legs of a radial cir uit connected to an MCB, but that is not two circuits. Also it is not bad practice.
CIRCUIT:
An assembly of electrical equipment supplied from the same origin and protected against overcurrent by the same protective device(s).
I think the arrangement above matches the description
I did wonder because the Design project limits you to circuits of 30m so I had several lighting circuit only rated about 2Amps I wondered in real life if I could in theory just put three of these say in to a single 6Amps MCB or maybe even more into a 10Amp MCB.
I think I'd be pushing my luck but couldn't find anything dangerous about it.
@JKMRK1
wow, look what you have started here!!
I like the conversation thread,
you are listed as a trainee, when you get your qualifications you will be a qualified electrician. just look at the different ways the regs have been interpreted and peoples opinions on what is good, bad and indifferent practice.
as your time and experience in the trade expands, you will start to build an idea of what is a good installation and will also be more opinionated about what is not ok.
bottom line for me when I consider things that are not accurately defined, would I be happy if this was installed at my daughters house?
it normally guides my mind in the right direction.
@JKMRK1
@JKMRK1
Tell me about it did think it would get so many mixed opinions!
Always tell myself it doesn't hurt to have a second opinion on things and as I wasnt certain about this that's what I done.
Thank you for the positive outlook and advice ?
Tell me about it did think it would get so many mixed opinions! Always tell myself it doesn't hurt to have a second opinion on things and as I wasnt certain about this that's what I done. Thank you for the positive outlook and advice ?
Wales
Trainee Electrician
Ring main.
JKMRK1,
Risteard,