Depending on the area (in square metres) extend the ring. Failing that then use a spare way and create another ring circuit.I'm not saying it's correct just saying what I've seen. That's why I've asked the question to make sure its correct.
[automerge]1588089613[/automerge]
Thanks for the advice it is much appreciated?
Probably don't have a spare way, that's why there are 2 RFCs crammed into one OCPD maybe?Depending on the area (in square metres) extend the ring. Failing that then use a spare way and create another ring circuit.
The short answer is electrically, if the rings comply in their own right with the regulations, they should be safe, but there are possibly implications with the installation not being split to minimise inconvenience and possibly danger from other factors (such as a loss of power to say life supporting equipment). It's unconventional and I don't think any of us would install like it, but certainly I would do it at a pinch to restore supply as a temporary measure.
This circuit might be described as a "butterfly" circuit.
Then settle for it being a final circuit which isn't a ring final circuit. Let's call it a double ring final circuit if you prefer. (Or call it a crap final circuit if you like - few will disagree.)Final circuit. A circuit connected directly to current-using equipment, or to a socket-outlet or socket-outlets or other
outlet points for the connection of such equipment.
Ring final circuit. A final circuit arranged in the form of a ring (not figure of eight) and connected to a single point of supply.
Well I called it a butterfly circuit, anybody can call it what they want, no problem. Just like the age old cooker circuit, modified cos cooker not needed so a ring produced from that point, some call that a "lolipop" circuit or a "lassoo" circuit (not implying a cowboy job I hope!). The butterfly or whatever you call it just like the lolipop can be a decent circuit designed using sound engineering judgement and be ok. The fact that they are not easily recognised as standard circuits does nothing to detract from that. It might confuse the unwary a little but you could ask "should they really be adding/modifying these circuits if they do not fully understand what they are doing?". Answer No, they could ask someone who does know though and there is no shame in that. There is no person who knows everything about everything.Then settle for it being a final circuit which isn't a ring final circuit. Let's call it a double ring final circuit if you prefer. (Or call it a crap final circuit if you like - few will disagree.)
I prefer to call them an abortion, work of the Devil.I would prefer to call them "Bow Tie" circuits sounds more sophisticated don't you know, can't get on with "lollipop" circuits sounds very childish, "Dragon fly" or a "Damselfly" at least they have four wings, can't think of a "Butterfly" with four wings.
hate to correct you there, but like bees, butterflies do have 4 wings.I would prefer to call them "Bow Tie" circuits sounds more sophisticated don't you know, can't get on with "lollipop" circuits sounds very childish, "Dragon fly" or a "Damselfly" at least they have four wings, can't think of a "Butterfly" with four wings.
I prefer to call them an abortion, work of the Devil.
Beginning to sound like Mumsnet.Am I on the right forum here?