Hi all,

DIYer here. My garage has a double socket fed by 4mm2 twin and earth connected to the same circuit breaker has the ring main for the sockets upstairs in the house. The MCB is a B32.

Is the feed in the garage considered a spur from the ring main or is it a separate radial circuit which happens to be on the same MCB? Ideally I'd like to add more sockets to the circuit in the garage (using 4mm2) but is this safe or allowed?

Thanks.
 
Just interested - how long is this 4mm spur cable?

Considering the 4mm is connected at one end at the CU (located in the garage) and to a socket at the other end (also located in the garage) I'm presuming it's not that long, unless the garage is massive and the route is silly.
 
Duel post, no idea why, apologies
 
Last edited:
Ah okay thanks for the reply, I did wonder, that explains your post :thumbsup:
It will be fine though
 
Is this because it's on a B32 MCB?
Considering the 4mm is connected at one end at the CU (located in the garage) and to a socket at the other end (also located in the garage) I'm presuming it's not that long, unless the garage is massive and the route is silly.

Perhaps its the same guy, who had the bathroom in his bedroom the other day; or was it a bedroom in his bathroom?
 
I wouldn't agree that the 4mm^2 part of the circuit needs to be considered as an unfused spur from the ring final circuit at all.

In my view it is clearly a hybrid ring/radial final circuit and in no way is it one of the standard circuits.

Assuming that the 4mm^2 cable is afforded overload protection by the 32A circuit breaker then it isn't unsafe to add sockets to the radial part of the hybrid circuit.

Presumably it was done because spare ways were not available or whatever. As I stated before my concern with the arrangement is solely the fact that there is unlikely to be an adequate connection/clamping of all the circuit conductors when they are of varying cross-sectional areas, and for this reason I would consider the arrangement to be wholly unsatisfactory.
 
As I stated before my concern with the arrangement is solely the fact that there is unlikely to be an adequate connection/clamping of all the circuit conductors when they are of varying cross-sectional areas, and for this reason I would consider the arrangement to be wholly unsatisfactory.

I wouldn't dismiss a connection of two different cable sizes out of hand. I think that it depends entirely on the skill and conscientiousness of the person doing the job and the type of terminal involved. I've seen a pigs ear made of terminating a standard 2.5mm² ring, and I've also made a decent job of terminating different cable sizes into the same terminal.
 
Thanks all.

Tempted to leave it as is for the time being and not add any additional sockets. There's a bathroom renovation on the cards soon where there is an electric shower running from a dedicated circuit. Once that has been decommissioned I'll ask he electrician to create a dedicated circuit for the garage sockets.
I think that this would be a good idea.
 
As I see it:
There is no need to apply the '1 point' limit to the radial. That limit is imposed to avoid overloading the spur cable (normally the same size as the ring cable and hence unprotected against overload by the OCPD) and to avoid concentrating the load on the ring itself at a single point partway along. Neither circumstance applies here as the 4mm² is not undersize for the OCPD nor connected partway along the ring.

I am with Risteard in that my only real concern would be the 2 x 2.5 + 1 x 4.0 terminated in the CU terminals. Whether it is likely any worse a connection than 3 x 2.5 not very nicely done in the back of a socket-outlet, is moot. It's not a standard circuit configuration and might automatically be non-compliant, unless the 'alternative methods of equal safety' concept applies.

I wouldn't say inserting an FCU in order to add more socket-outlets would make it materially safer. It might technically make it slightly less safe as the fuse in the FCU would be potentially prone to long slight overload as are all FCUs feeding multi-point spurs, a situation which ought to be avoided if possible, without offering any benefit to the protection of the circuit (which is already OK). It would however make it compliant apart from the possible objection to the mixed cables in the termination.
 

Reply to Ring spurred at origin? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
337
  • Question
Thanks for the advice.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top