F
foghorn
whlist testing a ring final socket circuit r1, rn and r2 end to9 end had all the same readings found a spur taken from the ring for an electric towel radiator remove the cpc from towel radiator and end to end test were spot on reconnect towel radiater and r2 end to end was reduced to virtulally equal to r1 and rn any thoughts on this would be appreciated.
so do u record the readings with towel rail disconnected as the cpc is no longer 1.67x more than r1, rn or record r2 at lower value which woulnt look right on eic
would it be worth mentioning the parallel bath in the coments section stating the towel radiator causing parallal path to explain unusual readings also lowerd the zs reading as well took zs with radiator cpc connected and without lowered the zs value
ring testing
foghorn,
Amp David,