F

foghorn

whlist testing a ring final socket circuit r1, rn and r2 end to9 end had all the same readings found a spur taken from the ring for an electric towel radiator remove the cpc from towel radiator and end to end test were spot on reconnect towel radiater and r2 end to end was reduced to virtulally equal to r1 and rn any thoughts on this would be appreciated.
 
would it be worth mentioning the parallel bath in the coments section stating the towel radiator causing parallal path to explain unusual readings also lowerd the zs reading as well took zs with radiator cpc connected and without lowered the zs value
 
so do u record the readings with towel rail disconnected as the cpc is no longer 1.67x more than r1, rn or record r2 at lower value which woulnt look right on eic

You are testing the Ring Final Circuit fixed wiring, not what is connected to it.
 

Reply to ring testing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
558
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
924

Similar threads

Very technical :D
    • Like
Replies
9
Views
563
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top