Had a call out to a home where the RCD keeps tripping when lounge ,dinning and bed room sockets mcb is switched on. Fault traced to one of the legs from the consumer unit to 1st socket 0.2Meg ohm at best. cable size is 2.5mm T&E there are 10 double and 4 single sockets on the circuit. Reg 433.1 seems to indicate that providing the floor area is limited to 50 m2 (the area in question is 3/4 the floor area of a medium size house. it would be ok to drop out the damaged leg from the consumer unit and socket fuse down to 20Amp mcb and leave as is. Possible to rewire initial leg and reinstate ring but do I need too?

what do you think?

AdieB

PS dropped leg out of consumer unit marked cable with tape and description of fault. Disconnected from socket and put wago type terminals on he cores. Changed mcb to16A (close's that was on van.)
 
If the installation socket outlet power requirements are below the new lower OCPD then leave it as a radial, thus avoiding disrupting the building fabric and further costs.

If higher current demands are required at a later date, then the ring can be reinstated or a new circuit installed.

Just my opinion.

The options should be provided to the client along with costs and implications.
 
So you have the option of reinstating the RFC or just disconnecting both ends of one leg.

Why not reinstate what is there leaving no cables loose in the back of a socket or DB. What happens when they decide to start plugging more appliances in, as believe me customers dont always tell the truth about what they have plugged in.
 
So you have the option of reinstating the RFC or just disconnecting both ends of one leg.

Why not reinstate what is there leaving no cables loose in the back of a socket or DB. What happens when they decide to start plugging more appliances in, as believe me customers dont always tell the truth about what they have plugged in.

charge them again for changing it back to a ring ;-) haha
 
One other thing OP have you done your cable calcs for volt drop and worked out if the Zs value will be compliant?

Pah.... making a right meal of it. Would you really sit there doing cable calcs for this?? I wouldn't. He can go at least 2.40 Zs on B16 60898. Experience would tell you, fit MCB and derate to radial, Quick Zs, MW, Done.
 
Pah.... making a right meal of it. Would you really sit there doing cable calcs for this?? I wouldn't. He can go at least 2.40 Zs on B16 60898. Experience would tell you, fit MCB and derate to radial, Quick Zs, MW, Done.

Well yes I would and I am pretty sure most others on here would do too.

Anyone that doesnt design every circuit they install is in my wyes just a chancer that thinks of nothing but lining their own pockets.
 
Well yes I would and I am pretty sure most others on here would do too.

Anyone that doesnt design every circuit they install is in my wyes just a chancer that thinks of nothing but lining their own pockets.

Charging unnecessary time is lining your pockets. Using your experience to save a customer money is not.
 

Reply to Ring to radial in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
732
  • Question
Why aren't you asking them?
Replies
5
Views
857

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top