Had a call out to a home where the RCD keeps tripping when lounge ,dinning and bed room sockets mcb is switched on. Fault traced to one of the legs from the consumer unit to 1st socket 0.2Meg ohm at best. cable size is 2.5mm T&E there are 10 double and 4 single sockets on the circuit. Reg 433.1 seems to indicate that providing the floor area is limited to 50 m2 (the area in question is 3/4 the floor area of a medium size house. it would be ok to drop out the damaged leg from the consumer unit and socket fuse down to 20Amp mcb and leave as is. Possible to rewire initial leg and reinstate ring but do I need too?
what do you think?
AdieB
PS dropped leg out of consumer unit marked cable with tape and description of fault. Disconnected from socket and put wago type terminals on he cores. Changed mcb to16A (close's that was on van.)