Points 1 - 7 have their pros.
Point 9, irrelevant.
Point 8, see my 1 point. Out doos the rest.
Point 9, irrelevant.
Point 8, see my 1 point. Out doos the rest.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Ring vs Radial in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
well so long as no-one takes my cheeky challenge too seriously , it may serve readers to think about all the design options in even simple domestic scenarios.
Rings...
If you get a break in the cpc, the whole cct still has an earth; cpc break on a radial, no earth beyond that point.
also takes much less typing for a convincing argument
i knew this as well widdler
one of the rings biggest advantages is also one of its biggest weaknesses.
but archy wasnt really up for reasoned debate lol.
If your +1 for a ring final requires a fault to be in the radial then look at it this way.
Radial.
Break in cpc = socket outlet with no cpc = risk of electric shock = RCD* disconnect when imbalance occurs.
Ring final.
Break in ring final = no detection of fault as only one line conductor has slipped out = 2 x 2.5mm cables with a best case scenario current carrying capacity of 27A (surface clipped) protected by a 32A MCB = Overloaded cable = House Fire = Death
*assuming this argument refers to scenarios where 30mA RCD's are required for socket outlets <20A.
:30::30::30::30::30::30::30::30:
A split ring, how often are you going to get >>20A down 1 leg for a significant length of time that it's going to fry a cable?
well if its a kitchen ring that has an undetected split , with the kettle , washing machine , dishwasher and tumble dryer and fan oven all fitted all close together on 1 wall of the kitchen , then its going to happen very frequently and for long periods.