Hi all, after some advise please.

I work as a maintenance engineer at a school and recently we had an outside contractor come in and fit an external Rolec EV unit to the outside of our workshop under the grant scheme.

I don't know much about the installation of these units but I did do part P several years ago so I have some electrical understanding. Consequently I do have some concerns about the installation which may be an issue or maybe more likely just my lack of knowledge!

The EV unit has the internal RCD for the AC supply, and the seperate RCD module for any DC injected back into the circuit. It has been installed with an internal isolator, meter and comms box which all seems fine.

However,

1) The contractors installed a new circuit in our DB for the EV supply but there is no test certificate to show results.

2) The unit is installed in our yard where we store gas cylinders and fuel. The charging unit has been installed directly above a metal storage unit that contains gerry cans of petrol. Gas cylinders are housed in a cage about 2 meters away.

3) The earth from the EV unit has been connected to the building's steel rainwater downpipe which goes under the ground but I've no idea how deep the pipe goes.

Are these issues cause for concern?

I'd appreciate your thoughts.

Many thanks.
 

Attachments

  • [ElectriciansForums.net] Rolec EV installation
    20191129_125054.jpg
    181.6 KB · Views: 68
  • [ElectriciansForums.net] Rolec EV installation
    20191129_125056.jpg
    216.4 KB · Views: 67
Regarding the earthing, it's been connected to the Lightning Protection which isn't ideal but if it's working properly it'll have an overall resistance to earth of less than 10 ohms. I presume you do have the LP system maintained?
 
2) The unit is installed in our yard where we store gas cylinders and fuel. The charging unit has been installed directly above a metal storage unit that contains gerry cans of petrol. Gas cylinders are housed in a cage about 2 meters away.
Surely someone from the school would have chosen the location for the charger.
 
Hi - hopefully whoever has engaged the Electrician has the Electrical Installation Certificate. It’d be interesting to see the loop impedance :) .
 
Hi - hopefully whoever has engaged the Electrician has the Electrical Installation Certificate. It’d be interesting to see the loop impedance :) .

You would think so, but at my place new circuits have been installed to supply some AC units in apartments, not a sniff of an EIC and we won't mention compliance certificates.

Edit By the by @Nuttyoak what supply do you have?
 
Surely someone from the school would have chosen the location for the charger.

Yeah, the bursar.
[automerge]1575058232[/automerge]
You would think so, but at my place new circuits have been installed to supply some AC units in apartments, not a sniff of an EIC and we won't mention compliance certificates.

Edit By the by @Nuttyoak what supply do you have?

The DB is 3 phrase which is run from the switch gear in the main plant room. The earth is also run from the plant room but I do not know what the earthing arrangement is at the incoming source. I do know we don't have our own sub station which is something we are apparently looking at because the site is so large in both the area it covers and the demand required. We've had issues with volt drop at the furthest corners of the school.
 
Last edited:
1 Yes an electrical installation certificate should have been completed and issued to the person ordering the work.

2 personally I think that is a daft place to install it and if I had been doing the job would definately have questioned the location. Whilst it should be absolutely fine and is unlikely to be a problem I would err on the side of caution.

3 it's not right, the lightning protection system should be bonded to the Electrical Installation at the main earth terminal and that bond should be connected underground at one of the earth rods. The odd connection they have made could cause a lightning strike to partially divert via the EV charger circuit.
If the LPS is correctly bonded then it will act as a very good earth electrode for the installation sufficient to allow even a PME earth to be used for the charger.

I suspect the installers take a one size fits all, monkey see - monkey do, approach to these installations without applying any thought to the job.
 
The odd connection they have made could cause a lightning strike to partially divert via the EV charger circuit.

And then into the car plugged into it....
We all know what happens when lightning hits a Delorian! 1985 here we come.
Great Scott, Marty!
 
I don't know the ins and outs of LPS which are essentially a stand alone safety system aside from the recent requirement for it to have a main protective bond to reduce pass over in the event of a fault, the chances of the original specification to allow it to be used for another purpose are all but zero.
[automerge]1575062676[/automerge]
Do you have a 12 monthly test of the LPS.
 
Last edited:
I don't know the ins and outs of LPS which are essentially a stand alone safety system aside from the recent requirement for it to have a main protective bond to reduce pass over in the event of a fault, the chances of the original specification to allow it to be used for another purpose are all but zero.
[automerge]1575062676[/automerge]
Do you have a 12 monthly test of the LPS.

Yeah, we do.
 

Reply to Rolec EV installation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
386
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
The last couple of de-loops that I have been involved with had the single phase supply replaced with a three phase cutout (as I believe the DNOs...
Replies
5
Views
1K
  • Question
This is a baffling fault I've been fighting with for a couple of weeks now, so I wondered if another set of eyes will help. I installed an EV...
Replies
0
Views
205

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top