Type B 60898 hager MCB 32A. MCB for Kitchen ring, trips when a few appliances are drawing load. ie, washing machine is running a cycle, kettle gets put on, and maybe toaster.
trip. (MCB only)
looked at this side of the kitchen. only one 2.5mm t&e comming from ceiling (must be jb unaccessable somewhere) to double socket above worktop. from this spur off to under counter lights. then spur to 3 single sockets under counter for various appliances then finally a double socket further over the counter.
all tests at fuse board fine insulation resistance, acceptable zs values, continuity of ring condictors etc.
now, r1+r2 readings 0.24, 0.28, 0.32, 0.44 at last point (double socket) confirms its a radial (spur off spur off spur)
over other side of kitchen readings of 0.05, 0.06 0.06/7.
as this 2.5mm cable has been spurred off 5 times would this be why its tripping MCB as cable is OVERLOADED?
i dont want to rewire whole ring final, for the same problem to occur. obviously!
am i on the right track here guys cheers!
trip. (MCB only)
looked at this side of the kitchen. only one 2.5mm t&e comming from ceiling (must be jb unaccessable somewhere) to double socket above worktop. from this spur off to under counter lights. then spur to 3 single sockets under counter for various appliances then finally a double socket further over the counter.
all tests at fuse board fine insulation resistance, acceptable zs values, continuity of ring condictors etc.
now, r1+r2 readings 0.24, 0.28, 0.32, 0.44 at last point (double socket) confirms its a radial (spur off spur off spur)
over other side of kitchen readings of 0.05, 0.06 0.06/7.
as this 2.5mm cable has been spurred off 5 times would this be why its tripping MCB as cable is OVERLOADED?
i dont want to rewire whole ring final, for the same problem to occur. obviously!
am i on the right track here guys cheers!