domestic spark

Type B 60898 hager MCB 32A. MCB for Kitchen ring, trips when a few appliances are drawing load. ie, washing machine is running a cycle, kettle gets put on, and maybe toaster.

trip. (MCB only)

looked at this side of the kitchen. only one 2.5mm t&e comming from ceiling (must be jb unaccessable somewhere) to double socket above worktop. from this spur off to under counter lights. then spur to 3 single sockets under counter for various appliances then finally a double socket further over the counter.

all tests at fuse board fine insulation resistance, acceptable zs values, continuity of ring condictors etc.

now, r1+r2 readings 0.24, 0.28, 0.32, 0.44 at last point (double socket) confirms its a radial (spur off spur off spur)

over other side of kitchen readings of 0.05, 0.06 0.06/7.

as this 2.5mm cable has been spurred off 5 times would this be why its tripping MCB as cable is OVERLOADED?

i dont want to rewire whole ring final, for the same problem to occur. obviously!


am i on the right track here guys cheers!
 
When you say a few appliances are these allat once , W/M heater 3kw , kettle 3kw 25a , toaster 2.3kw 9.98a total 34a does this circuit supply anything else? you say theres a JB in the ceiling have you checked to make sure it dosent feed the water heater or something stupid?
 
it happens when washing machine is on a cycle and kettle is put on or both kettle and toaster. for some reason half the kitchens been spurred.

KITCHEN RING on its own dedicated circuit.

im presuming JB hidden above ceiling as only one 2.5mm t&e drops down to double socket above worktop. from this spur off to under counter lights. then spur to 3 single sockets under counter for various appliances then finally a double socket further over the counter.

and radial confirmed by rising r1+r2 readings.

done a full test on circuit and all readings were ok.
 
would this cause a 32a breaker to trip though? by that i mean the only wrong thats happening here is, your overloading one 2.5 mm cable as your pulling way more than 27a through it, at best
 
needs further investigation. unplug all appliances in kitchen. clamp meter 1 leg of ring in CU. see if any current flow. clamp meter other leg . ditto. plug in one appliance at a time . meter both legs ( one then the other, not together. ). looks like a fair bit of rewiring needed. get rid of spurs. maybe the MCB has gone a bit tired after being heavily loaded for so long.
 
my logic was as ring has been spured 5x this is causing MCB to trip. my solution was to rewire to a proper ring, no spurs in 2.5 t&e and this would sort MCB tripping issue AM I WRONG?
 

Reply to scenaro in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

  • Locked
Thread closed.
2 3 4 5 6 7 8
Replies
110
Views
5K
Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
416

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top