Discuss Schneider board main switch TP-N and 4-pole in the UK Electrical Forum area at ElectriciansForums.net
Oh I thought there was a reason for the difference.The difference is one breaks the N the other doesn't.
What exactly do you want to know?
Oh I thought there was a reason for the difference.
Yes I'm trying to ask exactly that.Are you trying to ask why you would install one or the other?
Yes I'm trying to ask exactly that.
Thanks I'll have a look into it.There will be occasions where it is not desirable to break the neutral conductor along with the 3 line phases as doing so will present a more dangerous situation.
Have a read of Regulation 9 of EAWR .
There will be occasions where it is not desirable to break the neutral conductor along with the 3 line phases as doing so will present a more dangerous situation.
Yes I'm trying to ask exactly that.