You test the multicore and the plugs and sockets each end of it for all the normal dead tests - unplugged from any dimming - and do not even think about doing any live tests as even if you don't manage to destroy something then the results will be meaningless anyway.


I hope we're talking about installed rather than temporary installs so you do the usual tests you do for any installed circuit.

Treat an install dimmer as being another DB, only difference is doing the Zs test using the alternative method where you join L to E at the far end of the circuit and test between the incoming side of the dimmer and the outgoing.
 
4 ccts per hour over an 8-9 hour day onsite. If school was empty. 100%visual to every accessory 20%removal of accessories on circuit. And the use of common sense
 
100% in a domestic environment is a must but 100% in most commercial building's would be difficult to achieve to a acceptable price and disruption to the client. Previous test results and sufficient sampling of circuits should give anyone a indication to the extant of the test required
 
100% testing is acceptable but 100% internal inspection of equipment is not recommended as it can cause more damage and problems with the disturbance , especially if it is inspected regularly.
Sample inspections is the way to go, the extent of testing may be staged over time to reduce disruption.
 
So you would remove every accessory on a large ring main?

No, there are a few on here that do advocate 100% I & T I'm not one of them

100% in a domestic environment is a must but 100% in most commercial building's would be difficult to achieve to a acceptable price and disruption to the client. Previous test results and sufficient sampling of circuits should give anyone a indication to the extant of the test required

Why differentiate surely if it is good enough for one type of installation it is good enough for all.
 
I done a empty school last holidays, can do about 40 ccts a day--we do about 20% visual of accessories - if you find lots of faults you would increase the sampling.
 

Reply to School testing. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
534
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
916

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top