fair enough, I don't think I've ever done more than 3 tripowers on a circuit, so I've learned something today, thanks.from sma guidence only 3 inverters can be fitted on a 300ma type a rcd due to 90ma leakage from each inverter hence thats why the requirement for the four rcds ie 10 inverters .section 705 all circuits no more than 330ma on farms and nic guidence
eta - I've worked out where I went wrong there as well, thinking the earth leakage would be split across the 3 phases, but effectively the reverse is true.