Could you post the cable calc for the two options. IMO an external Cpc would be electrically preferential but I guess the brains at IET think otherwise.
I think there is a bit of confusion here, the thing I was trying to highlight was that the software said it was ok to use a 5c cable with an integral earth conductor, but not ok to use a 4c cable with a supplementary earth of the same size.
I have been thinking about this and and the only thing that comes to mind is the programme assuming the cpc will pass through a separate hole to the line conductors which would not happen if it were a core of the cable which may under fault conditions be problematic, maybe.