Is 0.06 ohms the max zs?
Did 300mm give you an R1+R2 of 0.04 ohms?
Did 300mm give you an R1+R2 of 0.04 ohms?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Seperate / Integral earth CPC on 400A supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I have been thinking about this and and the only thing that comes to mind is the programme assuming the cpc will pass through a separate hole to the line conductors which would not happen if it were a core of the cable which may under fault conditions be problematic, maybe.I think there is a bit of confusion here, the thing I was trying to highlight was that the software said it was ok to use a 5c cable with an integral earth conductor, but not ok to use a 4c cable with a supplementary earth of the same size.
Reply to Seperate / Integral earth CPC on 400A supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net