Hi guys, as the title suggest. Friend of mine buying a brand new house from a reputable and well established builder. however it has already been 1st fixed.
He\asked the builder if he could have an U/G supply taken out to the detached shed. Yes they could, no problem.
Method. To tap off the kitchen ring final circuit.
I would of thought a separate circuit from the house consumer unit would be required.
Is it still acceptable to tap of the ring final circuit? I know it used to be done that way years ago.
Thoughts please.
 
You should have asked for a separate supply for the shed. If it has not had the ceilings tacked this should still be possible. If they are coming off one of the RFC via a fused spur you will be limited to 13A I
would prefer to come off a lighter loaded circuit than maybe the kitchen ring.
 
Agree with other posts. Nothing wrong with it as long as its via 13a fused spur, but you are limited to 13a......also kitchen ring is usually heaviest loaded ring so chances of getting the full 13a in shed without overloading the circuit are small. But simple answer, nothing in regs against it.
 
If coming from the kitchen ring was the only reasonable option at this stage I'd run a 4mm 3 core SWA via a 1 gang 20a or 32a DP switch rather than a SFCU then terminate at a 2 way CU in the shed with a 16a and 6a MCB for the sockets and lights respectively.
I've put a small tin hat on now. :)
 
You should have asked for a separate supply for the shed. If it has not had the ceilings tacked this should still be possible. If they are coming off one of the RFC via a fused spur you will be limited to 13A I
would prefer to come off a lighter loaded circuit than maybe the kitchen ring.
Already first fixed
You should have asked for a separate supply for the shed. If it has not had the ceilings tacked this should still be possible. If they are coming off one of the RFC via a fused spur you will be limited to
It is something you can do yes. Switched FCU off ring main and ran in swa. Although not something I would do for many reasons

13A I
would prefer to come off a lighter loaded circuit than maybe the kitchen ring.
I would prefer a separate circuit myself
 

Reply to Shed supply from new build property in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K
Adding a led strip isn't going to make much difference to the 3 phase balance. No real difference to where a 3 phase machine uses one phase to...
Replies
2
Views
365

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top