New shower put in 9500 kw, 45 amp mcb as didn't have 40 on me & installed in 10mm cable. As soon as i pushed the power button on the shower the rcd tripped (it's an old hager board with one of those combined rcd/main switches) Everything is connected correctly, and before I pushed the power button I took a reading at the shower switch (supply side) and got 240v. Never got the chance to take a reading in the shower as I couldn't get in then due to other workers! Any ideas?
 
Ok. Update guys. Was back at the job today, flicked breaker back on and suprisingly it worked without tripping the rcd. Bit puzzled as done nothin' different from last time? Only thing i can think of is the suggestion that somebody had on friday concerning dampness as the cover had been left off. Thanks for takin' time out to reply anyway.
 

Reply to Shower fault... in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! âš¡ Please note that all EV Chargers and...
Replies
0
Views
106
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
905
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
639

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top