went to change three smoke alarms today and found they were wired in 1.5 t&e useing the cpc as the interconect link wire.
would you class this as a c1 / c2
i was thinking c1,
any thoughts
How old were the detectors?
>10 years then they need to be replaced, replacements being mains rf units..
I don’t see how the using the cpc can be a C1 or C2?
The interconnection is only 9 volts.
I would code it as a C3
I'd class it a C2. Where ADS is used the circuit requires a CPC. See 411.3.1.1 and GN8.
'A CPC shall be run to and terminated at each point in the wring and at each accessory point except a lamp holder having no exposed conductive parts and suspended from such a point'
The detectors may well be class 2 etc but the circuit still requires earthing.
essex
Business Name
forest plumbing and electrical installations
smoke alarm wiring.
Security Alarms, Door Entry and CCTV (Public)
tony clark,
sparks1234,