went to change three smoke alarms today and found they were wired in 1.5 t&e useing the cpc as the interconect link wire.
would you class this as a c1 / c2
i was thinking c1,
any thoughts
 
How old were the detectors?
>10 years then they need to be replaced, replacements being mains rf units..
I don’t see how the using the cpc can be a C1 or C2?
The interconnection is only 9 volts.
I would code it as a C3
 
I'd class it a C2. Where ADS is used the circuit requires a CPC. See 411.3.1.1 and GN8.

'A CPC shall be run to and terminated at each point in the wring and at each accessory point except a lamp holder having no exposed conductive parts and suspended from such a point'

The detectors may well be class 2 etc but the circuit still requires earthing.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
essex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
forest plumbing and electrical installations

Thread Information

Title
smoke alarm wiring.
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
27

Advert

Thread statistics

Created
tony clark,
Last reply from
sparks1234,
Replies
27
Views
3,954

Advert

Back
Top