I beg to differ, Reg 722.55.101.5 clearly states "The lowest part of any socket outlet shall be placed at a height of 0.5 to 1.5 m from the ground.
NOTE The requirements of the National Building Regulations should be adhered to in respect of socket outlet heights."

So there you have it, it's a departure, one way or another, and must be recorded.

That’s a section on car charging points so a big disagree
 
The point I was making is he caregorically said that Part M is entirely unrelated to compliance with BS7671 and I am showing him that he is wrong.

Vehicle charging points are defined in the Regs as street furniture. Reg 110 .1.1.
The note in this Reg is a general one referring to the Building Regulations.
 
Maybe I am wrong, but
  1. not sure why car chargers come into it
  2. that note is just pointing out that bs7671 doesn't overrule building regs in general, presumably to prevent confusion where building regs are stricter
  3. you can't have a deviation from building regulations as they are statutory laws
  4. although you do have to comply with part M on any material alteration to the accessories, you would achieve compliance as long as you don't make the situation worse than it was
but if the above four were all otherwise, yes you would be able to put it as a deviation.
 
I've looked at things from both sides now,
From in and out, but still somehow it's to the Regs I bow
(Apologies to Joni Mitchell)

Reg 553.01.06 "A socket-outlet on a wall or similar structure shall be mounted at a height above the floor or any working surface to minimize the risk of mechanical damage to the socket outlet or to an associated plug and its flexible cord which might be caused during insertion, use or withdrawal of the plug."

Part M of the Building Regulations (section 8) does not actually specify the required position but does go on to suggest that in habitable rooms this will be achieved by mounting the switches etc. between 45cm and 1.2m above the floor level.

Thank you all for helping me to rethink the whole thing. It's been interesting to see from the other persons side.
 
Last edited:
sometime s the problems come from ill-educated building inspectors. i once had a pratt insisted that cables fixed on a wall that was to be dry-lined must have capping.
 
I recently had this discussion with a guy on my crew at work who does kitchen renovations. Last year he did a kitchen refit for another crew member and he insisted that all the new sockets in the kitchen and new dinning room had to be at the ‘new build’ heights, so the customer has sockets at one end of the dinning room about 250-300mm from the floor and the other end they’re all at minimum of 450mm from the floor, there’s even 2 double sockets which are roughly 3ft from each other, 1 at 250mm & the other at 450mm, but he still insists that’s what ‘the rules say’, but based on some other photos I’ve seen, I don’t think he’s ever even owned a Lego set in his life. :) :) :)
 
I recently had this discussion with a guy on my crew at work who does kitchen renovations. Last year he did a kitchen refit for another crew member and he insisted that all the new sockets in the kitchen and new dinning room had to be at the ‘new build’ heights, so the customer has sockets at one end of the dinning room about 250-300mm from the floor and the other end they’re all at minimum of 450mm from the floor, there’s even 2 double sockets which are roughly 3ft from each other, 1 at 250mm & the other at 450mm, but he still insists that’s what ‘the rules say’, but based on some other photos I’ve seen, I don’t think he’s ever even owned a Lego set in his life. :) :) :)
he's a pr1ck.
 

Reply to Socket and switch heights in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
389
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
683
I would put this down to 433.3.1(ii) - no overload protection needed because the load at the single socket can't overload the cable, being fused...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top