MCBs whith higher instantaneous trip current values are used, where high start up currents are expected.
For example where there are DOL motors, lots of fluorescent lights, electric heaters, etc.
Yes I know Spin, the OP he asked about selection for general use S/O, I am aware he is from the US, but as far as I can gather he is certifying a product for Europe/UK, a type B gives a reasonable compromise for max Zs V inrush requirements, unless he has something specific in mind which may need a higher rated type.