For the eagle eyed out there, can you tell me whats wrong with this arrangement and for a bonus point what reg. no. would apply.

The only bit of info you need is that its a TT system. [ElectriciansForums.net] Spot what's wrong
 
Last edited:
Not to mention lack of earth fault protection, an RCBOs on their own aren't suitable for use on TT systems. In fact some manufacturers have it in bold print in their instructions that they aren't suitable.
 
I took the covers off to have a look
Ferrules not needed as the neutral fly leads come pre crimped

but yes your right about the up front RCD but only cos theres no grommet etc

RoB2 was the cover your one?

They don't look pre-crimped to me, in fact they look like they are splaying out. Maybe that's just the quality when I zoomed in.
 
This really is a poor install.

As to price guess, i can't see how many ways or rcbos but whats on show would be around ÂŁ400 + all his expert (teehee) time crimping dodgy cables etc so i'll go with ÂŁ1K !!! + VAT of course :)
 
They are manufactured so that you do not need to use ferrules.

Only if you need them to be that length, which you rarely do. Ferrules are required for all those that get shortened.

So if those RCBO tails are all the full length they are supplied at does that mean there is another fault of a load of neutral tails all bunched together getting nice and toasty?
 
Only if you need them to be that length, which you rarely do. Ferrules are required for all those that get shortened.

So if those RCBO tails are all the full length they are supplied at does that mean there is another fault of a load of neutral tails all bunched together getting nice and toasty?

well it looks like he threw the cables in so neatness was defo not his objective
 

Reply to Spot what's wrong in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
455
  • Question
If you are not lucky when adopting the 'just put it up and see what happens' approach then you will (ideally) need a uhf signal meter. As Brian...
Replies
2
Views
793

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top