Discuss Spot what's wrong in the UK Electrical Forum area at ElectriciansForums.net
Close 2K + VAT
11 circuits
Sorry had you go do a job.
Right the list of problems I noted were and you cant see most of then:
No neutral link between main switch and neutral bar therefore only single pole isolation on a TT system.
No grommet/ bush/gland for incoming tails therefore a RCD required as main switch or before board. If glanded correctly then RCD not needed as the meter is below
All lighting circuits have no cpc with metal switches and lights in use. Even through the cable entering the board has cpc. Under the board theres a piece of 2x2 plastic trunking stuffed full of the old cables all thro crimped to extend into new board. The old cable has no cpc but new cable does.
No testing was done before or after the install.
No labels except RCD warning (I no some of you dont like labels but its in the book)
No circuit chart
Someone made a note re ring circuits but all circuits do have RCBO's but in picture you cant see the left hand side fully.
Take a stab at how much he was charged and any thoughts on the reg no yet.
Do you?
So you don't need a 300ma upfront.
I'm pulling your leg.
Just don't want the inexperienced thinking it's the only option.