For the eagle eyed out there, can you tell me whats wrong with this arrangement and for a bonus point what reg. no. would apply.

The only bit of info you need is that its a TT system. [ElectriciansForums.net] Spot what's wrong
 
Last edited:
Sorry had you go do a job.

Right the list of problems I noted were and you cant see most of then:

No neutral link between main switch and neutral bar therefore only single pole isolation on a TT system.
No grommet/ bush/gland for incoming tails therefore a RCD required as main switch or before board. If glanded correctly then RCD not needed as the meter is below
All lighting circuits have no cpc with metal switches and lights in use. Even through the cable entering the board has cpc. Under the board theres a piece of 2x2 plastic trunking stuffed full of the old cables all thro crimped to extend into new board. The old cable has no cpc but new cable does.
No testing was done before or after the install.
No labels except RCD warning (I no some of you dont like labels but its in the book)
No circuit chart

Someone made a note re ring circuits but all circuits do have RCBO's but in picture you cant see the left hand side fully.

Take a stab at how much he was charged and any thoughts on the reg no yet.

Still Need an UP front 300ma RCD on a TT system
 

Yes its A TT system so see Reg 411.5.2 ,also see table 41.5.which will show if the earth loop impedance is 167 or less then a 300mA RCD will do the Job , I suggested 300ma as Earth loop reading from a earth Rods generally around the 70 to 100 Ohm mark, off course if you are getting a much lower reading say if the structural steel is being used and the ZS is low enough then you could get away with just over current protection reg 411.5.2 (ii) and to be fare I did jump to conclusions as the op stated it was a TT system and most TT systems are above the permitted ZS for an over current device , but from experience of ground conditions changing over time I would go for the 300ma , which also would give you the disconnection of the neutral and so solving the original deviation of on un-switched neutral
 

Reply to Spot what's wrong in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
439
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
244
I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
461

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top