p/262 . Uufused ↔ Spur . is Protected by .. 2 – 13A Fuses ( 1 – Double Socket ) & Yes Eath Loop Impedance / Volt Drop
Page 362
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Spur From Ring in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
p/262 . Uufused ↔ Spur . is Protected by .. 2 – 13A Fuses ( 1 – Double Socket ) & Yes Eath Loop Impedance / Volt Drop
so an easy solution would be to reduce the ring final MCB from 32A to 25A? rather than adding an enclosed MCB just for the spur.Taking from IET
cable is 3 meters or less you may protect it on the end of the cable rather than the source see 433.2.2. Since a 13 amp socket has to have 13 amp fuses in the plug then a 2.5mm cable feeding a single 13 amp outlet either with one or two sockets in it is considered as being protected by the fuses in the plug. Hence the use of spurs from ring mains. Over 3 meters then it would need protecting as source hence a radial with one socket would need a 25 amp MCB mainly because it is over 3 meters cable run. Is that what you were asking and what is an RF circuit?
Am not turning this in to an AGUMENT . Full Stop .
* Unfused Spur . the Two are different .
* Fused Spurs
this is way it ends .
It's a discussion!
I'm not arguing but if someone posts that the maximum length for an unfused spur is 3 Metres then I dispute it because it simply is not true!
And it ends when a few more people read this thread and confirm that I'm absolutely correct.
Thanks Guys, that was a great exchange, followed it with interest, not clear on the outcome,
IF a double socket on a spur IS pulling 26 amps, how is the single 2.5 protected?
In best case scenario, the 2.5 will handle 27 Amps but in reality, the socket outlet will fail long before the cable.
Most twin outlets are rated at 20A with MK being a known exception at 26A.
The installation design in your scenario would need to be altered to suit the excess load.
True, but punters don't know this, in a domestic installation where a spur is used in this way, and I can see it happening on cold nights when the C/H is on the blink, what then? if the cable shorts or the double socket melts we can't call that circuit protected can we?
You still have fault protection and overcurrent protection but the BS 1363 socket standard rates an outlet whether twin or single at 13A plus an additional short time test at 20A for a twin (14A in one side, 6A in the other).
I suppose the danger is no greater in a socket on the ring final itself, subject to the same BS 1363 standard.
Reply to Spur From Ring in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net