Srur it?
growler
Another trivial topic but here goes... iv been asked to install a security light in a back garden, switch will be located by back door above worktop. there is already a spur (kitchen ring) next to where the switch will go. Just pondering whether to take easy option and spur of ring or take a feed from kitchen light and keep lights seperate? probably a no brainer!
existing socket is allowed as an unfused spur. a fused spur should by rights be fitted before that socket and then a 3A FCU from that. however, whilst unconventional, i can't see a problem with fitting a 3A FCU after the unfused spur socket.
Tel, I quite agree with you but the books and guidance say otherwise! lol
key word is guidance. such an arrangement would be just as safe as if the guidance ( BS7671 ) was followed to the letter and so i stand by it. some may disagree. opinions welcome.
my argument exactly. it's basically drawing an extra max. of 3A over and above the assumed 20A load of the spurred socket, i.e 23A max. on 2.5mm cable rated at 27A ( ref. method C).
spur from a spur!
Murdoch
I don't think it means that kind of spur, I thought it referred to a socket outlet on a RFC. Clearly a spur off a spur off a spur is ok on a radial.
However in this case i would sleep soundly, but can also see the point- a spurred DG socket at full load on a single piece of 2.5 is ... At full tilt so no room for an extra bit on the end......would be ok though if the spurred DG socket was supplied by ref method 'free air' (30A). :-))
security light generally will be 400 or 500 watt, still only a couple of amps , though.
I'm only playing devils advocate - you know, its a no, no to do a spur off a spur whilst common sense clearly sees and calculates that the load on the spur will be well under the capacity of the cable!!
why? it's a no.no to add an unfused spur off a spur. where's the reg. says you can't take a fused spur off an unfused spur
growler,
needasparks,
TrueNAS JBOD Storage Server